Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-17 04:06 AM
good morning
I tried to update the firmware of the AP8653 using NMC "firmware update utility", the update was not successful and I can no longer log in from the browser. I can only log in with SSH.
How can i restore firmware ?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-23 02:09 AM
Hello,
Finally I found the solution. In case the AP8653 firmware update failed, " Stat :P+ N4+ N6+ A-," I performed the boot factory reset procedure, and then uploaded the updated firmware files via Xmodem as described here: https://www.apc.com/us/en/faqs/FA293874/
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-17 05:54 AM
Hello @carmelo71, thank you for your question! We'll come back to you 🙂
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-23 02:09 AM
Hello,
Finally I found the solution. In case the AP8653 firmware update failed, " Stat :P+ N4+ N6+ A-," I performed the boot factory reset procedure, and then uploaded the updated firmware files via Xmodem as described here: https://www.apc.com/us/en/faqs/FA293874/
Link copied. Please paste this link to share this article on your social media post.