Voltage transformer burden calculation

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Voltage transformer burden calculation
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
71
J_Travostino
Sisko J_Travostino Sisko
70
S-W
Commander S-W Commander
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Solved
MohamedIbrahim
Ensign MohamedIbrahim Ensign
Ensign

Posted: ‎2021-08-30 03:20 AM

1 Like
6
9582
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-30 03:20 AM

Voltage transformer burden calculation

Dears, 

 

I'm working in a project and it's required to create VT calculation and We have the following issue:

 

The calculated burden is around 8 VA while the VT burden is 100VA and as per IEC 61869-3  clause number 5.6.301&302 it's mandatory to guarantee that the calculated burden of the VT is between 25% to 100% of the rated output burden.

 

The problem here that the VT is already purchased with VT burden 100VA, Thanks to advise about the accuracy?? or there is any solution for eradicate this problem without changing the Purchased VT.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
RHH
Commander | EcoXpert Master RHH Commander | EcoXpert Master
Commander | EcoXpert Master

Posted: ‎2021-09-23 11:57 PM . Last Modified: ‎2021-09-24 12:01 AM

2 Likes
3
9468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-09-23 11:57 PM . Last Modified: ‎2021-09-24 12:01 AM

I agree with @MathieuGuillot,

 

The IEC norm is probably used for measurements. As far as I know with measurements, you dont want to have a way lower output as it will influence your accuracy in measurement as the transformer is made for a certain use/output to measure most accurately.

For such specifics I use the internet for help, maybe the site beneath could help you relate better in what you want/need to do;

(Its for Power transformers, but might be usefull nonetheless)
https://www.electrical-installation.org/enwiki/Choice_of_transformer_rating


Kind regards,

Rick

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

MohamedIbrahim
Ensign MohamedIbrahim Ensign
Ensign

Posted: ‎2021-10-05 03:02 AM

In response to RHH
1 Like
2
9409
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-05 03:02 AM

Dear ,

 

I already find a solution by testing the accuracy of these VT's with the calculated burden in ALCE (VT supplier) and it's found that :



• SEE instruct their sub-supplier to test one 11 KV PT with a lower burden value of 3.75 VA (lower than 25% of the burden) and they found that the PT is in limits of Class1.0 at the test which is considered as a minor impact.


• SEE instruct their sub-supplier to test one 6.6 KV PT with a lower burden value of 8.35 VA (lower than 25% of the burden) and they found that the PT is in limits of Class1.0 at the test which is considered as a minor impact.


•the supplier confirmed that the protection core of all VT' will not be affected.

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
MathieuGuillot
Lieutenant MathieuGuillot Lieutenant
Lieutenant

Posted: ‎2021-09-17 06:50 AM

1 Like
0
9523
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-09-17 06:50 AM

Hello

 

What are these VT used for ? 

 

You need accuracy for revenue metering but if the VT are only providing voltage measurement as a basic indication of for Over/undervotage protection the accuracy you have with a low burden is probably not an issue.

 

 

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

RHH
Commander | EcoXpert Master RHH Commander | EcoXpert Master
Commander | EcoXpert Master

Posted: ‎2021-09-23 11:57 PM . Last Modified: ‎2021-09-24 12:01 AM

2 Likes
3
9469
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-09-23 11:57 PM . Last Modified: ‎2021-09-24 12:01 AM

I agree with @MathieuGuillot,

 

The IEC norm is probably used for measurements. As far as I know with measurements, you dont want to have a way lower output as it will influence your accuracy in measurement as the transformer is made for a certain use/output to measure most accurately.

For such specifics I use the internet for help, maybe the site beneath could help you relate better in what you want/need to do;

(Its for Power transformers, but might be usefull nonetheless)
https://www.electrical-installation.org/enwiki/Choice_of_transformer_rating


Kind regards,

Rick
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

MohamedIbrahim
Ensign MohamedIbrahim Ensign
Ensign

Posted: ‎2021-10-05 03:02 AM

In response to RHH
1 Like
2
9410
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-05 03:02 AM

Dear ,

 

I already find a solution by testing the accuracy of these VT's with the calculated burden in ALCE (VT supplier) and it's found that :



• SEE instruct their sub-supplier to test one 11 KV PT with a lower burden value of 3.75 VA (lower than 25% of the burden) and they found that the PT is in limits of Class1.0 at the test which is considered as a minor impact.


• SEE instruct their sub-supplier to test one 6.6 KV PT with a lower burden value of 8.35 VA (lower than 25% of the burden) and they found that the PT is in limits of Class1.0 at the test which is considered as a minor impact.


•the supplier confirmed that the protection core of all VT' will not be affected.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

RHH
Commander | EcoXpert Master RHH Commander | EcoXpert Master
Commander | EcoXpert Master

Posted: ‎2021-10-05 03:23 AM

In response to MohamedIbrahim
1 Like
0
9399
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-05 03:23 AM

Hello @MohamedIbrahim,

Thats great to see, thanks for letting us know the road you've taken to your acceptable and on paper certified/calculated answer!

Good luck!


Kind regards,

Rick
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

EhabAbdou
EhabAbdou
Cadet

Posted: ‎2023-03-18 10:11 PM

0 Likes
0
6750
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-18 10:11 PM

Hello @MohamedIbrahim 

I facing the same issue in substation, could you please advise if you have been solved this issue.

can you please if you have a solution contact me in eng.ehabmostafa@gmail.com 

Reply

Link copied. Please paste this link to share this article on your social media post.

asif1
asif1
Cadet

Posted: ‎2024-10-22 03:53 AM

In response to MohamedIbrahim
0 Likes
0
2077
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-22 03:53 AM

True .... but the original VT was Class 0.2.  If its working accuracy is class 1, then its a loss.  Anyhow, it doesn't matter because nobody will look into design errors as long as there is no catastrophic failure....  Rest assured, in next project as well 100 VA VT will be procured

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now