Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Will 400 V three Phase system work with a supply of 380V three Phase

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Will 400 V three Phase system work with a supply of 380V three Phase
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
80
J_Travostino
Sisko J_Travostino Sisko
70
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Expert on Demand for Standards & Regulations

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2020-08-29 01:44 AM . Last Modified: ‎2020-11-20 03:53 AM

0 Likes
2
9874
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-08-29 01:44 AM . Last Modified: ‎2020-11-20 03:53 AM

Will 400 V three Phase system work with a supply of 380V three Phase

We have a juice Production line working with a rating voltage of 400 V three phase. it is planned to be moved to another country having a voltage rating of 380 V three phase. 

 

will it work there efficiently? or it needs modifications. 

 

Thanks 

Mohammad Obaidat 

Labels
  • Labels:
  • Connectivity
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
MathieuGuillot
Lieutenant MathieuGuillot Lieutenant
Lieutenant

Posted: ‎2020-09-02 04:48 AM

3 Likes
1
9831
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-02 04:48 AM

 

Hello,

I don’t see any risk of major malfunction during operation at 380Vac nominal voltage for a system designed for 400Vac. Indeed large majority of equipment designed for 400Vac are applicable to 380Vac. But as we say “The Devil is in the Details.”

 

To ensure proper functioning of the future installation you should check few things:

  • I suggest to start your analysis by checking the tolerances of the supply voltage in both locations. What is the minimum voltage you may have today and what is the minimum voltage you may have tomorrow.  If the tolerance of the supply in your new location is -10% you have to check that your production line can withstand temporary operation at 340Vac LL 200Vac LN.  But may be your existing system is 400Vac -10% and the future 380Vac – 5% …
  • When you know the minimum voltage you can reach in the future, global efficiency and performance will depend on the type of loads.
    • Some loads have a current proportional to the voltage (Typically resistor like heaters ..) for this loads the voltage reduction will means current reduction. From process point of view it will means longer operation for an heater to reach the same temperature.
    • Some loads have a constant power, so voltage reduction means current increase. (Typically electronic converters such as variable speed drive, electronic power supply …) In that case there is no consequence on the process itself, but the supply and electrical equipment (cables, circuit-breaker, contactors…) upstream such loads need to handle the increase of the current. (Risk is overload trip for instance)
    • Some loads have a more complex relationship between voltage and current : typically induction motors. Reduction of the voltage implies reduction of the torque applied to the mechanical loads. This may have an impact on your process (less debit for pump, less pressure for a juicer …) depending on the type of mechanical load. Here again at 380Vac nominal it shall not have significant consequence as 380V is in the tolerance of a 400Vac system. But if the 380Vac system is running at – 5 or -10% you may start to have consequences on your process.
    • Some equipment have a “black and white behavior” according to voltage : typically relay / contactors .. that will switch off below a limit. You have to check that this type of equipment are able to operate as expected in the full range of voltage.

 

Hope it helps.

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
MathieuGuillot
Lieutenant MathieuGuillot Lieutenant
Lieutenant

Posted: ‎2020-09-02 04:48 AM

3 Likes
1
9832
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-02 04:48 AM

 

Hello,

I don’t see any risk of major malfunction during operation at 380Vac nominal voltage for a system designed for 400Vac. Indeed large majority of equipment designed for 400Vac are applicable to 380Vac. But as we say “The Devil is in the Details.”

 

To ensure proper functioning of the future installation you should check few things:

  • I suggest to start your analysis by checking the tolerances of the supply voltage in both locations. What is the minimum voltage you may have today and what is the minimum voltage you may have tomorrow.  If the tolerance of the supply in your new location is -10% you have to check that your production line can withstand temporary operation at 340Vac LL 200Vac LN.  But may be your existing system is 400Vac -10% and the future 380Vac – 5% …
  • When you know the minimum voltage you can reach in the future, global efficiency and performance will depend on the type of loads.
    • Some loads have a current proportional to the voltage (Typically resistor like heaters ..) for this loads the voltage reduction will means current reduction. From process point of view it will means longer operation for an heater to reach the same temperature.
    • Some loads have a constant power, so voltage reduction means current increase. (Typically electronic converters such as variable speed drive, electronic power supply …) In that case there is no consequence on the process itself, but the supply and electrical equipment (cables, circuit-breaker, contactors…) upstream such loads need to handle the increase of the current. (Risk is overload trip for instance)
    • Some loads have a more complex relationship between voltage and current : typically induction motors. Reduction of the voltage implies reduction of the torque applied to the mechanical loads. This may have an impact on your process (less debit for pump, less pressure for a juicer …) depending on the type of mechanical load. Here again at 380Vac nominal it shall not have significant consequence as 380V is in the tolerance of a 400Vac system. But if the 380Vac system is running at – 5 or -10% you may start to have consequences on your process.
    • Some equipment have a “black and white behavior” according to voltage : typically relay / contactors .. that will switch off below a limit. You have to check that this type of equipment are able to operate as expected in the full range of voltage.

 

Hope it helps.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Gregoire_Brun
Commander Gregoire_Brun Commander
Commander

Posted: ‎2022-02-01 07:14 AM . Last Modified: ‎2022-02-01 07:16 AM

In response to MathieuGuillot
1 Like
0
8591
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-01 07:14 AM . Last Modified: ‎2022-02-01 07:16 AM

in line with @MathieuGuillot .

Please take care of the frequenly (50hz or 60 hz)  of the network too

Gregoire Brun
Breaker Product Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore