Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82374members
349871posts

Will 400 V three Phase system work with a supply of 380V three Phase

Power Distribution and Digital

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Solved
m_obaidat
Cadet
0 Likes
2
2227

Will 400 V three Phase system work with a supply of 380V three Phase

We have a juice Production line working with a rating voltage of 400 V three phase. it is planned to be moved to another country having a voltage rating of 380 V three phase. 

 

will it work there efficiently? or it needs modifications. 

 

Thanks 

Mohammad Obaidat 

Tags (1)

Accepted Solutions
MathieuGuillot
Lieutenant Lieutenant
Lieutenant

Re: Will 400 V three Phase system work with a supply of 380V three Phase

 

Hello,

I don’t see any risk of major malfunction during operation at 380Vac nominal voltage for a system designed for 400Vac. Indeed large majority of equipment designed for 400Vac are applicable to 380Vac. But as we say “The Devil is in the Details.”

 

To ensure proper functioning of the future installation you should check few things:

  • I suggest to start your analysis by checking the tolerances of the supply voltage in both locations. What is the minimum voltage you may have today and what is the minimum voltage you may have tomorrow.  If the tolerance of the supply in your new location is -10% you have to check that your production line can withstand temporary operation at 340Vac LL 200Vac LN.  But may be your existing system is 400Vac -10% and the future 380Vac – 5% …
  • When you know the minimum voltage you can reach in the future, global efficiency and performance will depend on the type of loads.
    • Some loads have a current proportional to the voltage (Typically resistor like heaters ..) for this loads the voltage reduction will means current reduction. From process point of view it will means longer operation for an heater to reach the same temperature.
    • Some loads have a constant power, so voltage reduction means current increase. (Typically electronic converters such as variable speed drive, electronic power supply …) In that case there is no consequence on the process itself, but the supply and electrical equipment (cables, circuit-breaker, contactors…) upstream such loads need to handle the increase of the current. (Risk is overload trip for instance)
    • Some loads have a more complex relationship between voltage and current : typically induction motors. Reduction of the voltage implies reduction of the torque applied to the mechanical loads. This may have an impact on your process (less debit for pump, less pressure for a juicer …) depending on the type of mechanical load. Here again at 380Vac nominal it shall not have significant consequence as 380V is in the tolerance of a 400Vac system. But if the 380Vac system is running at – 5 or -10% you may start to have consequences on your process.
    • Some equipment have a “black and white behavior” according to voltage : typically relay / contactors .. that will switch off below a limit. You have to check that this type of equipment are able to operate as expected in the full range of voltage.

 

Hope it helps.

See Answer In Context

Tags (1)
2 Replies 2
MathieuGuillot
Lieutenant Lieutenant
Lieutenant

Re: Will 400 V three Phase system work with a supply of 380V three Phase

 

Hello,

I don’t see any risk of major malfunction during operation at 380Vac nominal voltage for a system designed for 400Vac. Indeed large majority of equipment designed for 400Vac are applicable to 380Vac. But as we say “The Devil is in the Details.”

 

To ensure proper functioning of the future installation you should check few things:

  • I suggest to start your analysis by checking the tolerances of the supply voltage in both locations. What is the minimum voltage you may have today and what is the minimum voltage you may have tomorrow.  If the tolerance of the supply in your new location is -10% you have to check that your production line can withstand temporary operation at 340Vac LL 200Vac LN.  But may be your existing system is 400Vac -10% and the future 380Vac – 5% …
  • When you know the minimum voltage you can reach in the future, global efficiency and performance will depend on the type of loads.
    • Some loads have a current proportional to the voltage (Typically resistor like heaters ..) for this loads the voltage reduction will means current reduction. From process point of view it will means longer operation for an heater to reach the same temperature.
    • Some loads have a constant power, so voltage reduction means current increase. (Typically electronic converters such as variable speed drive, electronic power supply …) In that case there is no consequence on the process itself, but the supply and electrical equipment (cables, circuit-breaker, contactors…) upstream such loads need to handle the increase of the current. (Risk is overload trip for instance)
    • Some loads have a more complex relationship between voltage and current : typically induction motors. Reduction of the voltage implies reduction of the torque applied to the mechanical loads. This may have an impact on your process (less debit for pump, less pressure for a juicer …) depending on the type of mechanical load. Here again at 380Vac nominal it shall not have significant consequence as 380V is in the tolerance of a 400Vac system. But if the 380Vac system is running at – 5 or -10% you may start to have consequences on your process.
    • Some equipment have a “black and white behavior” according to voltage : typically relay / contactors .. that will switch off below a limit. You have to check that this type of equipment are able to operate as expected in the full range of voltage.

 

Hope it helps.

Tags (1)
Gregoire_Brun
Lt. Commander Lt. Commander
Lt. Commander

Re: Will 400 V three Phase system work with a supply of 380V three Phase

in line with @MathieuGuillot .

Please take care of the frequenly (50hz or 60 hz)  of the network too