What type of breakers are more effective for solar solutions?

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • What type of breakers are more effective for solar solutions?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
80
J_Travostino
Sisko J_Travostino Sisko
70
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Expert on Demand for Standards & Regulations

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Start a Topic
Solved
Elec_
Crewman Elec_
Crewman

Posted: ‎2025-04-15 12:37 AM

1 Like
2
2164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-15 12:37 AM

What type of breakers are more effective for solar solutions?

Hey everyone,

I'm looking into setting up a solar power system and need some advice on the best type of circuit breakers to use. I've heard that there are different types.

Can anyone share their experiences or recommendations on which type is more effective for solar solutions? Any tips on what to consider when choosing the right breaker would be super helpful!

Thanks in advance!

Labels
  • Labels:
  • How to
  • Knowledge
  • Products
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Manon_Chaboud
Commander Manon_Chaboud Commander
Commander

Posted: ‎2025-04-15 05:11 AM

2 Likes
0
2102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-15 05:11 AM

Hello @Elec_, 

 

When selecting circuit breakers for solar solutions, it's essential to consider the specific needs of your solar power system. Circuit breakers play a crucial role in protecting solar installations from electrical faults, ensuring safety, and optimizing performance. 

 

There are two types of circuit breakers for Solar Solutions:

  1.  DC Circuit Breakers: these are designed to handle direct current (DC) from solar panels. They are essential for protecting the DC side of the system, preventing damage from overcurrents and short circuits.
  2. AC Circuit Breakers: these breakers protect the alternating current (AC) side of the system. They ensure that any faults in the AC circuit are quickly isolated to prevent damage and maintain safety.

 

When choosing a breaker, consider the following factors:

- System requirements: understand the voltage and current ratings needed for your system.

- Environmental factors: ensure the breaker can withstand the environmental conditions where it will be installed.

- Compliance with standards: verify that the breaker conforms to relevant standards such as IEC 60947-2.

 

Our recommended product: EasyPact MVST3

For those looking for a reliable and high-performance solution, the EasyPact MVS T3 is an excellent choice. Here are some of its standout features:

- One frame size: simplifies installation and maintenance.

- Current rating: up to 4000A, suitable for large-scale solar installations.

- Voltage rating: Ue up to 1140V AC, with IT 800V AC applicable (annex H compliant).

- High breaking capacity: Ics=100%Icu=Icw=66KA, ensuring robust protection.

- Intelligent electronic protection system: enhances safety and efficiency.

- Compliance: conforms to IEC 60947-2, ensuring adherence to international standards.

- Wide range of accessories: offers flexibility and customization for various applications.

 

Additionally, the EasyPact Solar MCCB is another great option, providing scalable and reliable protection for renewable energy applications. It features:

- Current rating: up to 800A.

- High breaking capacity: up to 50kA.

- Insulation voltage: 1250V AC.

- TM & ETU releases: for precise protection settings.

- Wide range of accessories: enhances versatility and ease of use.

 

For more detailed information and to explore the full range of products, you can check out the catalogs attached.

 

By carefully selecting the right circuit breakers, you can ensure the safety, reliability, and efficiency of your solar power system.

 

Best regards,

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Manon_Chaboud
Commander Manon_Chaboud Commander
Commander

Posted: ‎2025-04-15 05:11 AM

2 Likes
0
2103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-15 05:11 AM

Hello @Elec_, 

 

When selecting circuit breakers for solar solutions, it's essential to consider the specific needs of your solar power system. Circuit breakers play a crucial role in protecting solar installations from electrical faults, ensuring safety, and optimizing performance. 

 

There are two types of circuit breakers for Solar Solutions:

  1.  DC Circuit Breakers: these are designed to handle direct current (DC) from solar panels. They are essential for protecting the DC side of the system, preventing damage from overcurrents and short circuits.
  2. AC Circuit Breakers: these breakers protect the alternating current (AC) side of the system. They ensure that any faults in the AC circuit are quickly isolated to prevent damage and maintain safety.

 

When choosing a breaker, consider the following factors:

- System requirements: understand the voltage and current ratings needed for your system.

- Environmental factors: ensure the breaker can withstand the environmental conditions where it will be installed.

- Compliance with standards: verify that the breaker conforms to relevant standards such as IEC 60947-2.

 

Our recommended product: EasyPact MVST3

For those looking for a reliable and high-performance solution, the EasyPact MVS T3 is an excellent choice. Here are some of its standout features:

- One frame size: simplifies installation and maintenance.

- Current rating: up to 4000A, suitable for large-scale solar installations.

- Voltage rating: Ue up to 1140V AC, with IT 800V AC applicable (annex H compliant).

- High breaking capacity: Ics=100%Icu=Icw=66KA, ensuring robust protection.

- Intelligent electronic protection system: enhances safety and efficiency.

- Compliance: conforms to IEC 60947-2, ensuring adherence to international standards.

- Wide range of accessories: offers flexibility and customization for various applications.

 

Additionally, the EasyPact Solar MCCB is another great option, providing scalable and reliable protection for renewable energy applications. It features:

- Current rating: up to 800A.

- High breaking capacity: up to 50kA.

- Insulation voltage: 1250V AC.

- TM & ETU releases: for precise protection settings.

- Wide range of accessories: enhances versatility and ease of use.

 

For more detailed information and to explore the full range of products, you can check out the catalogs attached.

 

By carefully selecting the right circuit breakers, you can ensure the safety, reliability, and efficiency of your solar power system.

 

Best regards,

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Gregoire_Brun
Commander Gregoire_Brun Commander
Commander

Posted: ‎2025-04-16 12:38 AM

2 Likes
0
2020
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-16 12:38 AM

Hello @Elec_ 

To complete @Manon_Chaboud answer, Key factors to consider include the network connection (DC/AC) and the voltage range (from 415V to 1000V for AC, and from 48V to 1500V for DC), as well as the short circuit capability.

Another important aspect is the integration constraint. Few panel builders offer panels that are certified for 800V or 1000V, making it a challenge to obtain such certifications.

Environmental constraints are also significant due to the ambient temperature, which can affect the breaker. The load percentage seen by the breaker can be higher than in distribution systems, so it is crucial to choose the right derating applicable to the product.

Gregoire Brun
Breaker Product Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore