What is the maximum allowable temperature on the terminals of a MTZ ACB?
  • Power Distribution IEC
  • What is the maximum allowable temperature on the terminals of a MTZ ACB?
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
80
J_Travostino
Sisko J_Travostino Sisko
70
cdurand
cdurand Cadet
Cadet
Posted: ‎2023-03-10 11:27 AM
2
1051
Gregoire_Brun
Commander
Posted: ‎2023-04-06 11:53 PM
hello @cdurand
this point is define on the IEC 60-947-1
On a Brand new product, for silver contact (case of MTZ) maximum temperature on terminals is 110°C maximum.
Gregoire Brun
Breaker Product Expert
Gregoire_Brun
Commander
hello @cdurand
Gregoire Brun
RJ-Rahul
RJ-Rahul
Cadet
Posted: ‎2025-12-09 10:54 AM
Could you please confirm the maximum permissible temperature at the terminals for your switch disconnectors (specifically NSX 400NA) and miniature circuit breakers (MCBs) under normal operating conditions?
I noticed that the ambient air temperature for operation is specified as a maximum of 70 °C for the switch disconnector. Does this imply that the incoming cable to this device need be downrated to operate at 70 °C?
Additionally, are there any links or guidance documents that outline the maximum terminal temperature for protective devices?