What is the burden calculation of a voltage transformer?
  • Power Distribution IEC
  • What is the burden calculation of a voltage transformer?
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
80
J_Travostino
Sisko J_Travostino Sisko
70
Manon_Chaboud
Commander Manon_Chaboud Commander
Commander
Posted: ‎2025-03-13 02:58 AM
1
1456
Properly calculating the burden could secure that the voltage transformer operates within its specified limits and provides accurate voltage measurements to the connected devices.
Calculating the burden of a voltage transformer involves determining the maximum load that can be connected to the secondary side of the transformer without adversely affecting its performance.
The burden is typically expressed in volt-amperes (VA) and includes the total impedance of the connected burden, which consists of the impedance of measuring instruments, relays, and secondary wiring.
The burden can be calculated using the formula: Burden (VA) = (Secondary Voltage)^2 / (Impedance of the connected burden)
It's also important to consider both the resistive and reactive components of the impedance when calculating the burden.
Here are some tools can simply help you on the calculation:
  • Electrical calculation tool
  • Discover EcoStruxure Power Design – Ecodial
  • How to
  • Knowledge
RHH
Commander | EcoXpert Master RHH Commander | EcoXpert Master
Posted: ‎2025-03-18 01:16 AM
With (smaller) transformers always check the VA load of the relais and/or other components behind it to ensure you have the right amount of VA on the output of your transformer. If your components together pull too much, choose for a bigger/higher output transformer.
Kind regards,
Rick