Ecodial 5.3.1 - Total coordination with 4kW motor not possible

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Ecodial 5.3.1 - Total coordination with 4kW motor not possible
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
71
J_Travostino
Sisko J_Travostino Sisko
70
S-W
Commander S-W Commander
65
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Power Design – Ecodial

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Solved
ZR
Crewman ZR
Crewman

Posted: ‎2025-01-22 10:54 PM

0 Likes
6
470
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-22 10:54 PM

Ecodial 5.3.1 - Total coordination with 4kW motor not possible

Hi to All,

 

I can't select the Total coordination in the motor wizard for 4kW direct motor drive.

For other power ratings it works fine.

Does anyone else have the same problem?

 

BR,

Zarko  

Labels
  • Labels:
  • EcoStruxure Power Commission (EPC)
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Saravanakumar.L
Lieutenant Saravanakumar.L Lieutenant
Lieutenant

Posted: ‎2025-02-06 11:57 PM

In response to ZR
0 Likes
2
315
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-06 11:57 PM

Hello ZR, 

 

Thank you for sending the project.

 

We have validated the project and noted that a different protection device has been selected, and the cross-section of the cables varies.

 

Specifically, the cable for WD3 is 50 meters, while for WD4, it is 5 meters, resulting in different cross-sections.

SaravanakumarL_0-1738914739102.png

 

The choice of the protection device is based on the motor load starter operation characteristics, which differ from one another.

SaravanakumarL_1-1738914926984.png

SaravanakumarL_2-1738914962937.png

 

 

Therefore, the protection device must respond based on the specific load requirements.

 

We have the coordination data for the two motor loads and their starters and have adopted the protection as expected.

 

I hope this clarifies your query.

 

Thanks & Regards, 

Team- Ecodial Expert Support. 

 

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Saravanakumar.L
Lieutenant Saravanakumar.L Lieutenant
Lieutenant

Posted: ‎2025-03-18 02:52 AM

In response to ZR
0 Likes
0
150
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-18 02:52 AM

Hello ZR, 

 

Thanks for reaching us!

 

We have validated the query from our side, and this may implement in upcoming release according to business

priority. 

 

The next version may release in August 2025. 

 

Thanks & Regards,

Team- Ecodial expert support 

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Manon_Chaboud
Commander Manon_Chaboud Commander
Commander

Posted: ‎2025-01-23 09:07 AM

0 Likes
0
440
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-23 09:07 AM

Hello @ZR, thank you for your question§

@Saravanakumar.L, can you advise @ZR please? 

Thank you in advance!

Reply

Link copied. Please paste this link to share this article on your social media post.

Saravanakumar.L
Lieutenant Saravanakumar.L Lieutenant
Lieutenant

Posted: ‎2025-01-27 09:48 PM

0 Likes
4
402
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-27 09:48 PM

Hello Zarco, 

 

Thanks for reaching us 

 

Please share the project/Ecodial file for analyze the issue. 

 

Thanks & Regards,

Team- Ecodial Expert Support. 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

ZR
Crewman ZR
Crewman

Posted: ‎2025-01-29 02:09 AM

In response to Saravanakumar.L
0 Likes
3
386
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-29 02:09 AM

Hello Saravanakumar,

 

Please find project attached.

 

As you will see, two identical 4kW motors are configured, one with a direct starter and the other with a reverse starter. When configuring with the wizard, you can select Total coordination with reversible starter and only Type 1 or Type 2 with direct starter.
As a consequence, a different protection device is selected and the cross-section of the cable is different.

BR,
Zarko

Attachments
Ecodial 5.3.1 - Motor load 4kW total coordination 20250129.eac
Reply

Link copied. Please paste this link to share this article on your social media post.

Saravanakumar.L
Lieutenant Saravanakumar.L Lieutenant
Lieutenant

Posted: ‎2025-02-06 11:57 PM

In response to ZR
0 Likes
2
316
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-06 11:57 PM

Hello ZR, 

 

Thank you for sending the project.

 

We have validated the project and noted that a different protection device has been selected, and the cross-section of the cables varies.

 

Specifically, the cable for WD3 is 50 meters, while for WD4, it is 5 meters, resulting in different cross-sections.

SaravanakumarL_0-1738914739102.png

 

The choice of the protection device is based on the motor load starter operation characteristics, which differ from one another.

SaravanakumarL_1-1738914926984.png

SaravanakumarL_2-1738914962937.png

 

 

Therefore, the protection device must respond based on the specific load requirements.

 

We have the coordination data for the two motor loads and their starters and have adopted the protection as expected.

 

I hope this clarifies your query.

 

Thanks & Regards, 

Team- Ecodial Expert Support. 

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

ZR
Crewman ZR
Crewman

Posted: ‎2025-02-07 04:22 AM

In response to Saravanakumar.L
0 Likes
1
297
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-07 04:22 AM

Dear all,

 

Thank you for your explanation.

I wanted to point out that for a 4kW DOL starter Total coordination cannot be selected in the motor wizard and consequently Tesys U LUB12 is not a possible solution.

Total coordination can be selected for any other motor except 4kW. It can even be selected for 4kW reverse motor.

In the project I sent, my mistake was not to use the same cable lengths for both drives, which distracted from the real issue.

 

BR,

ZR

Reply

Link copied. Please paste this link to share this article on your social media post.

Saravanakumar.L
Lieutenant Saravanakumar.L Lieutenant
Lieutenant

Posted: ‎2025-03-18 02:52 AM

In response to ZR
0 Likes
0
151
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-18 02:52 AM

Hello ZR, 

 

Thanks for reaching us!

 

We have validated the query from our side, and this may implement in upcoming release according to business

priority. 

 

The next version may release in August 2025. 

 

Thanks & Regards,

Team- Ecodial expert support 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of