What does "upstream" and "downstream" mean in a circuit breaker?

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • What does "upstream" and "downstream" mean in a circuit breaker?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
80
J_Travostino
Sisko J_Travostino Sisko
70
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Expert on Demand for Standards & Regulations

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-03-13 01:56 AM

3 Likes
9
33767
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-13 01:56 AM

What does "upstream" and "downstream" mean in a circuit breaker?

Hello,

 

I have seen several times the words "upstream" and "downstream" related to circuit breakers. 

 

Can someone explain me simply and clearly what these mean?

Is there any difference with supply & load for circuit breaker?

 

Sorry if this question may seem a little weird to you .... 😊 😁

 

 

Thanks a lot.

 

 

Labels
  • Labels:
  • How to
  • Products
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-03-13 03:52 AM

2 Likes
7
33746
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-13 03:52 AM

Hello,

 

In Electrical Distribution, upstream and downstream refers to "Incoming" and "outgoing" circuit breakers.

 

Regarding your question on supply and load of circuit breaker, there is no supply side and load side in present circuit breakers 

and supply and load connections  can be reversed. In Earlier circuit breakers, there was specific marking on circuit breaker i.e.

terminals were marked with Supply or Load side, Technology has progressed and these connections can be reversed.

 

Hope I answer your question.

 

Thanks.

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

RHH
Commander | EcoXpert Master RHH Commander | EcoXpert Master
Commander | EcoXpert Master

Posted: ‎2022-02-01 12:32 PM . Last Modified: ‎2022-02-01 12:42 PM

In response to Anonymous user
2 Likes
1
31494
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-01 12:32 PM . Last Modified: ‎2022-02-01 12:42 PM

Hello @Anonymous user 

The breakers with those limitations have the indications on the devices.
Breakers who dont have this do not show this indication as it is not necessary.

As far as I know;

The breakers who can have these limitations are mostly breakers like;

An GFCI Circuit breaker - Ground-Fault circuit interruptor
An AFCI/D Circuit breaker - Arc-Fault circuit interruptor/detector

Why are those limitations especially on these breakers? Because they have an extra security build in where they have to react/trip/turn off to.

With this security in the products they are more susceptible to damage or fault-trips if they are connected reversed.

At last, the picture you ask about how it can be marked below;
LINE-LOAD.jpg
Sometimes it is shown on a label on the breaker as well; No reverse feeding!

But like the previous answer; You barely see this anymore as the fabrication of breakers have evolved with the years.

Hope this is of any help to you!

 

 


Kind regards,

Rick

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Gregoire_Brun
Commander Gregoire_Brun Commander
Commander

Posted: ‎2022-02-02 11:28 PM . Last Modified: ‎2025-08-12 05:13 AM

In response to Anonymous user
2 Likes
1
31459
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-02 11:28 PM . Last Modified: ‎2025-08-12 05:13 AM

hello

It's due to some performance limitation in some products to respect performance during short circuit test.

It's the case for Compact NSX R, HB1, HB2 (690V application and the new NSX400K (1000V Application)

 

I will see to find some pictures to find equivalent picture shared by RHH-Eltechna

 

Best regards

Gregoire Brun
Breaker Product Expert

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
J_Travostino
Sisko J_Travostino Sisko
Sisko

Posted: ‎2021-03-13 02:03 AM

1 Like
0
33752
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-13 02:03 AM

Hello @Anonymous user 

 

Do not worry. There is no "stupid" question.

 

Someone from our community will surely be able to answer you on this..... 😉

 

Julien Travostino
Power Distribution & Digital forum community owner
Power Products Div.
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-03-13 03:52 AM

2 Likes
7
33747
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-13 03:52 AM

Hello,

 

In Electrical Distribution, upstream and downstream refers to "Incoming" and "outgoing" circuit breakers.

 

Regarding your question on supply and load of circuit breaker, there is no supply side and load side in present circuit breakers 

and supply and load connections  can be reversed. In Earlier circuit breakers, there was specific marking on circuit breaker i.e.

terminals were marked with Supply or Load side, Technology has progressed and these connections can be reversed.

 

Hope I answer your question.

 

Thanks.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-03-13 09:29 AM

In response to Anonymous user
0 Likes
6
33738
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-13 09:29 AM

Thank you @Anonymous user for your quick answer. 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Gregoire_Brun
Commander Gregoire_Brun Commander
Commander

Posted: ‎2022-02-01 07:18 AM . Last Modified: ‎2022-02-01 07:20 AM

In response to Anonymous user
0 Likes
5
31521
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-01 07:18 AM . Last Modified: ‎2022-02-01 07:20 AM

Hello @Anonymous user  

On catalogue we speak about some limitation sometime about reverse feeding ( for some high perf breaker)

And we indicate on the breaker if it have limitation the "line" side for upstream and "load " side for downstream

 

 

Gregoire Brun
Breaker Product Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2022-02-01 07:47 AM

In response to Gregoire_Brun
0 Likes
4
31513
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-01 07:47 AM

Thank you @Gregoire_Brun for these complementary information.

 

What are the criteria for these limitations? 

Which products are concerned?

 

What do you mean "we indicate on the breaker"? I guess it is like some marking but can you confirm and eventually post a picture?

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

RHH
Commander | EcoXpert Master RHH Commander | EcoXpert Master
Commander | EcoXpert Master

Posted: ‎2022-02-01 12:32 PM . Last Modified: ‎2022-02-01 12:42 PM

In response to Anonymous user
2 Likes
1
31495
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-01 12:32 PM . Last Modified: ‎2022-02-01 12:42 PM

Hello @Anonymous user 

The breakers with those limitations have the indications on the devices.
Breakers who dont have this do not show this indication as it is not necessary.

As far as I know;

The breakers who can have these limitations are mostly breakers like;

An GFCI Circuit breaker - Ground-Fault circuit interruptor
An AFCI/D Circuit breaker - Arc-Fault circuit interruptor/detector

Why are those limitations especially on these breakers? Because they have an extra security build in where they have to react/trip/turn off to.

With this security in the products they are more susceptible to damage or fault-trips if they are connected reversed.

At last, the picture you ask about how it can be marked below;
LINE-LOAD.jpg
Sometimes it is shown on a label on the breaker as well; No reverse feeding!

But like the previous answer; You barely see this anymore as the fabrication of breakers have evolved with the years.

Hope this is of any help to you!

 

 


Kind regards,

Rick
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2022-02-01 11:37 PM

In response to RHH
1 Like
0
31480
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-01 11:37 PM

Thank you @RHH for sharing information. 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Gregoire_Brun
Commander Gregoire_Brun Commander
Commander

Posted: ‎2022-02-02 11:28 PM . Last Modified: ‎2025-08-12 05:13 AM

In response to Anonymous user
2 Likes
1
31460
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-02 11:28 PM . Last Modified: ‎2025-08-12 05:13 AM

hello

It's due to some performance limitation in some products to respect performance during short circuit test.

It's the case for Compact NSX R, HB1, HB2 (690V application and the new NSX400K (1000V Application)

 

I will see to find some pictures to find equivalent picture shared by RHH-Eltechna

 

Best regards

Gregoire Brun
Breaker Product Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2022-02-03 12:58 AM

In response to Gregoire_Brun
0 Likes
0
31454
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-03 12:58 AM

Thanks @Gregoire_Brun 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore