Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-13 01:56 AM
Hello,
I have seen several times the words "upstream" and "downstream" related to circuit breakers.
Can someone explain me simply and clearly what these mean?
Is there any difference with supply & load for circuit breaker?
Sorry if this question may seem a little weird to you .... 😊 😁
Thanks a lot.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-13 03:52 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-13 03:52 AM
Hello,
In Electrical Distribution, upstream and downstream refers to "Incoming" and "outgoing" circuit breakers.
Regarding your question on supply and load of circuit breaker, there is no supply side and load side in present circuit breakers
and supply and load connections can be reversed. In Earlier circuit breakers, there was specific marking on circuit breaker i.e.
terminals were marked with Supply or Load side, Technology has progressed and these connections can be reversed.
Hope I answer your question.
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-02-01 12:32 PM . Last Modified: 2022-02-01 12:42 PM
Hello @T_Parks
The breakers with those limitations have the indications on the devices.
Breakers who dont have this do not show this indication as it is not necessary.
As far as I know;
The breakers who can have these limitations are mostly breakers like;
An GFCI Circuit breaker - Ground-Fault circuit interruptor
An AFCI/D Circuit breaker - Arc-Fault circuit interruptor/detector
Why are those limitations especially on these breakers? Because they have an extra security build in where they have to react/trip/turn off to.
With this security in the products they are more susceptible to damage or fault-trips if they are connected reversed.
At last, the picture you ask about how it can be marked below;
Sometimes it is shown on a label on the breaker as well; No reverse feeding!
But like the previous answer; You barely see this anymore as the fabrication of breakers have evolved with the years.
Hope this is of any help to you!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-02-02 11:28 PM
hello
It's due to some performance limitation in some products to respect performance during short circuit test.
It's the case for Compact NSX R, HB1, HB2 (690V application and the new NSX400K (1000V Application)
I will see to find some pictures to find equivalent picture shared by RHH-Eltechna
Best regards
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-13 03:52 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-13 03:52 AM
Hello,
In Electrical Distribution, upstream and downstream refers to "Incoming" and "outgoing" circuit breakers.
Regarding your question on supply and load of circuit breaker, there is no supply side and load side in present circuit breakers
and supply and load connections can be reversed. In Earlier circuit breakers, there was specific marking on circuit breaker i.e.
terminals were marked with Supply or Load side, Technology has progressed and these connections can be reversed.
Hope I answer your question.
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-02-01 07:18 AM . Last Modified: 2022-02-01 07:20 AM
Hello @T_Parks
On catalogue we speak about some limitation sometime about reverse feeding ( for some high perf breaker)
And we indicate on the breaker if it have limitation the "line" side for upstream and "load " side for downstream
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-02-01 07:47 AM
Thank you @Gregoire_Brun for these complementary information.
What are the criteria for these limitations?
Which products are concerned?
What do you mean "we indicate on the breaker"? I guess it is like some marking but can you confirm and eventually post a picture?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-02-01 12:32 PM . Last Modified: 2022-02-01 12:42 PM
Hello @T_Parks
The breakers with those limitations have the indications on the devices.
Breakers who dont have this do not show this indication as it is not necessary.
As far as I know;
The breakers who can have these limitations are mostly breakers like;
An GFCI Circuit breaker - Ground-Fault circuit interruptor
An AFCI/D Circuit breaker - Arc-Fault circuit interruptor/detector
Why are those limitations especially on these breakers? Because they have an extra security build in where they have to react/trip/turn off to.
With this security in the products they are more susceptible to damage or fault-trips if they are connected reversed.
At last, the picture you ask about how it can be marked below;
Sometimes it is shown on a label on the breaker as well; No reverse feeding!
But like the previous answer; You barely see this anymore as the fabrication of breakers have evolved with the years.
Hope this is of any help to you!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-02-02 11:28 PM
hello
It's due to some performance limitation in some products to respect performance during short circuit test.
It's the case for Compact NSX R, HB1, HB2 (690V application and the new NSX400K (1000V Application)
I will see to find some pictures to find equivalent picture shared by RHH-Eltechna
Best regards
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.