WTG contactor
  • Power Distribution IEC
  • WTG contactor
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
80
J_Travostino
Sisko J_Travostino Sisko
70
TeSys Deca contactors
sukantnh
sukantnh
Cadet
Posted: ‎2024-03-19 11:57 PM
1093
WTG contactor
Hi  I need your advice for below
 One of the WTG manufacturer has suggested 3 pole contactors per phase for LV side of transformer. these contactors are 1400 A rated , 3 in parallel will able to deliver 3x1400 A = 4200 A for stator circuit .
Is these an acceptable solution if not what is the disadvantage and is there any guideline/ standards which prevents it.
I am attaching the details of the circuit for understanding.
Sukant
Mr
  • India Power Distribution & Digital
Manon_Chaboud
Commander Manon_Chaboud Commander
Commander
Posted: ‎2024-09-19 01:33 AM
2
920
Hello @sukantnh !
Using multiple contactors in parallel to achieve a higher current rating is generally not recommended. The main disadvantage is the potential for unbalanced current sharing among the contactors, leading to uneven wear and tear, and potential safety hazards.
It's important to refer to relevant standards like IEC 60947 for LV switchgear and control gear, as well as manufacturer's guidelines, to ensure compliance and safe operation. It's advisable to consult with a qualified electrical engineer to find the most suitable and compliant solution for the application.
Manon_Chaboud
Commander
2
921
Hello @sukantnh !
sukantnh
sukantnh
Cadet
Posted: ‎2024-09-19 04:35 AM
In response to Manon_Chaboud
905
Dear Manon,
Thanks for your reply, your reply is matching my understanding and quite reasonable.
Best Regards
Sukant
Mr
S-W
Commander S-W Commander
Commander
Posted: ‎2024-10-03 08:16 AM
In response to sukantnh
@sukantnh: Thank you for the message for @Manon_Chaboud, we 're glad that the solution works on your end. Thank you and please have a lovely day.