Tutorial: How to size a transformer for industrial loads?

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Tutorial: How to size a transformer for industrial loads?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
80
J_Travostino
Sisko J_Travostino Sisko
70
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Expert on Demand for Standards & Regulations

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Power Distribution and Digital Support
Start a Topic
Manon_Chaboud
Commander Manon_Chaboud Commander
Commander

Posted: ‎2025-07-09 01:15 AM . Last Modified: ‎2025-07-09 01:17 AM

0 Likes
0
774
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-09 01:15 AM . Last Modified: ‎2025-07-09 01:17 AM

Tutorial: How to size a transformer for industrial loads?

Correctly sizing a transformer is essential for ensuring reliable power delivery, avoiding overloads, and planning for future expansion.

Follow this step-by-step guide to determine the right transformer size for your industrial application.

 

Step 1: list all electrical loads

Start by identifying all the equipment that will be powered by the transformer. For each item, note:

  • Power rating (in kW, kVA, or HP)
  • Voltage
  • Phase (single or three-phase)
  • Operating current (if available)

Step 2: convert all loads to kVA

Transformers are rated in kVA, so convert all loads accordingly:

  • For three-phase loads:
    kVA = (√3 × Voltage × Current) / 1000
  • For single-phase loads:
    kVA = (Voltage × Current) / 1000

If you only have kW and power factor (PF): kVA = kW / PF

 

Step 3: apply demand and diversity factors

Not all equipment runs at full load all the time. Apply:

  • Demand factor: reflects the actual maximum load expected.
  • Diversity factor: accounts for the probability that not all loads operate simultaneously.

Example:
If your total connected load is 500 kVA and the demand factor is 0.8:
Actual load = 500 × 0.8 = 400 kVA

 

Step 4: add a safety margin

To allow for future expansion and avoid overloading, add a safety margin of 10–25%.

Example:
Required transformer size = 400 × 1.2 = 480 kVA

 

Step 5: select the nearest standard transformer size

Choose the next standard transformer size above your calculated requirement.

Common sizes include: 25, 50, 75, 100, 150, 200, 300, 500, 750, 1000 kVA, etc.

In the example above, you would choose a 500 kVA transformer.

 

Step 6: match voltage levels

Ensure the transformer’s:

  • Primary voltage matches the utility supply
  • Secondary voltage matches your equipment requirements

Step 7: consider additional factors

  • Cooling type: dry-type (indoor) or oil-immersed (outdoor)
  • Impedance: affects short-circuit current levels
  • Efficiency: higher efficiency reduces energy losses
  • Environmental conditions: temperature, humidity, altitude, etc.

 

In conclusion, proper transformer sizing is essential for ensuring safe, efficient, and reliable power distribution in industrial settings. By calculating the total load, applying realistic demand factors, and including a safety margin, you can confidently select a transformer that meets both current and future needs. Always match voltage levels and consider environmental and operational factors to ensure long-term performance.

Labels
  • Labels:
  • How to
  • Knowledge
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore