Posted: 2024-10-18 12:53 AM
Trihal dry-type transformer 2250KVA
Can the Trihal dry-type transformer, rated at 2250 kVA from Schneider Electric, operate continuously at 110% of its nominal power capacity? Could you share any documentation that proves this?
- Tags:
- english
Authentication Failed.
- Authentication Ticket Mismatched, failed authentication.
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-30 02:42 AM
Hello @tienphat21.
We have the final answer of the experts from the global level 🙂
According to IEC 60076-11 standard, the rated power of transformer is the maximum power for continuous operation.
If overload is needed, there is the IEC 60076-12 which specify the calculation of maximum overload according to the previous load of transformer in steady state.
Other possibility is requesting a transformer for a capacity of continuous overload of 110%, then on this case the transformer will be designed to delivery the additional power without over crossthe limits of rise temperature.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-18 05:42 AM
Hello @tienphat21, thank you for your question! We will come back to you.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-20 05:31 AM
Hello Ms @Manon_Chaboud,
Thank you so much for your response! I really appreciate your prompt attention to my inquiry. I’m eagerly looking forward to receiving the relevant information and documentation, as it would greatly help me in preparing for a tender submission to our customer. If possible, could you kindly provide the details by tomorrow?
Thanks again, and I look forward to hearing from you soon!
Best regards,
Phat - ESEC
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-20 11:09 PM
Dear Ms @Manon_Chaboud
I hope this message finds you well. I wanted to kindly follow up on the information regarding the Trihal dry-type transformer, rated at 2250 kVA. The details and documentation would be extremely helpful as I am currently preparing for a tender submission to a customer.
If possible, could you please provide the relevant details by tomorrow? Your support is greatly appreciated.
Thank you once again for your assistance, and I look forward to hearing from you soon!
Best regards,
Phat - ESEC
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-21 04:23 AM
Hello @tienphat21, your request is in progress with the related expert, I'll come back to you ASAP, thank you for your understanding 🙂 Have a good day!
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-29 05:26 AM
Hello @tienphat21, I apologize for the delay... Your request is in process at the global level but I also recommend you contact your country's CCC (Customer Care Center) if it's urgent. Have a good day 🙂
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-30 02:42 AM
Hello @tienphat21.
We have the final answer of the experts from the global level 🙂
According to IEC 60076-11 standard, the rated power of transformer is the maximum power for continuous operation.
If overload is needed, there is the IEC 60076-12 which specify the calculation of maximum overload according to the previous load of transformer in steady state.
Other possibility is requesting a transformer for a capacity of continuous overload of 110%, then on this case the transformer will be designed to delivery the additional power without over crossthe limits of rise temperature.