Transformers and power distribution

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Transformers and power distribution
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
80
J_Travostino
Sisko J_Travostino Sisko
70
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Expert on Demand for Standards & Regulations

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2020-09-07 07:26 AM . Last Modified: ‎2020-11-20 03:53 AM

1 Like
3
2791
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-07 07:26 AM . Last Modified: ‎2020-11-20 03:53 AM

Transformers and power distribution

I need some clarification on transformers and power distribution. The transformer is marked 75 4800, a second unit 167 4800 and a third unit 25 4800.

I am assuming this is 167 kVA (or 75 or 25) and the primary voltage is 4800. Am I correct?

Since our secondary voltage is 120VAC and there is 3-wires coming from the transformer, am I correct to assume this is a center tap and we have 1 phase 2 poles? If this is correct and the transformer is in fact 25kVA, does that mean each pole has 25kVA or the whole transformer is 25kVA and each pole effectively delivers 1/2 the rated value. Thus at 120VAC does each pole have 208 A or 104 A.

Labels
  • Labels:
  • Connectivity
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
mjk68
Ensign mjk68 Ensign
Ensign

Posted: ‎2020-09-08 07:43 AM

2 Likes
2
2770
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-08 07:43 AM

There are some unknowns here, so the below are assumptions with the given values. With the secondary voltage of 120 and the markings of 25, 75, and 167 - I would assume as you have stated that these are the kVA ratings and the 4800 is more than likely the primary voltage. Additionally, the 3-wires are either a center tapped winding, or a 2-winding transformer connected internally and only 1 connection lead brought out of the transformer. In either case the secondary voltage would be 120/240 based on your ampacity values stated above. The formula to calculate Full-Load Current with Single-Phase Transformer is = kVA x 1000 / V

Using the 25kVA transformer as an example:

25 x 1000 / 120 = 208 secondary amps or
25 x 1000 / 240 = 104 secondary amps

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

mjk68
Ensign mjk68 Ensign
Ensign

Posted: ‎2020-09-08 01:16 PM . Last Modified: ‎2020-09-09 06:06 AM

In response to Anonymous user
2 Likes
0
2757
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-08 01:16 PM . Last Modified: ‎2020-09-09 06:06 AM

200A would be the overall circuit ampacity and not a 100A per pole additive equation statement. The measured voltage of 240 volts would be between each pole or phase and the measured voltage of 120 volts would be from either phase to the center-tap wire. If all the connected loads were balanced the measured amps would be equal.

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
mjk68
Ensign mjk68 Ensign
Ensign

Posted: ‎2020-09-08 07:43 AM

2 Likes
2
2771
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-08 07:43 AM

There are some unknowns here, so the below are assumptions with the given values. With the secondary voltage of 120 and the markings of 25, 75, and 167 - I would assume as you have stated that these are the kVA ratings and the 4800 is more than likely the primary voltage. Additionally, the 3-wires are either a center tapped winding, or a 2-winding transformer connected internally and only 1 connection lead brought out of the transformer. In either case the secondary voltage would be 120/240 based on your ampacity values stated above. The formula to calculate Full-Load Current with Single-Phase Transformer is = kVA x 1000 / V

Using the 25kVA transformer as an example:

25 x 1000 / 120 = 208 secondary amps or
25 x 1000 / 240 = 104 secondary amps

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-09-08 12:38 PM

In response to mjk68
0 Likes
1
2759
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-08 12:38 PM

Thanks for the response, and your assumptions where as mine.

 

However, the confusing part for me is the panel box.  There is a 200A 2-pole main breaker.  So does each pole have 200A or is it 100A?

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

mjk68
Ensign mjk68 Ensign
Ensign

Posted: ‎2020-09-08 01:16 PM . Last Modified: ‎2020-09-09 06:06 AM

In response to Anonymous user
2 Likes
0
2758
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-08 01:16 PM . Last Modified: ‎2020-09-09 06:06 AM

200A would be the overall circuit ampacity and not a 100A per pole additive equation statement. The measured voltage of 240 volts would be between each pole or phase and the measured voltage of 120 volts would be from either phase to the center-tap wire. If all the connected loads were balanced the measured amps would be equal.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore