Arc Protection I/O unit error

Power Distribution and Digital

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Solved
NiMo
Crewman
Crewman
3
1141

Arc Protection I/O unit error

Hi.

We received two arc protection I/O unit (VAM12LSE), both with same error.

 

When we turned on the I/O units with 24VDC power supply, the error indicator is turned on and (unlike other sensor inputs) LED of sensor input no. 4 is blinking, without any arc sensor connection to it.

In addition, if we connect an arc sensor to input 4, the corresponding LED is turned off.

in the following link you can find the corresponding recorded movie.

https://drive.google.com/file/d/1Yy5CSUbXgMbq2OHYv-HU_1H_KcP8z8un/view?usp=sharing

https://drive.google.com/file/d/1hN5Eykmp_J_EKtlYXFkCZ9jDjlUaQAsa/view?usp=sharing

 

can anyone help us to find the problem?

 

Vam12LSE.jpg

Tags (2)

Accepted Solutions
H_ERSHADZADEH
Lieutenant JG Lieutenant JG
Lieutenant JG
2
1029

Re: Arc Protection I/O unit error

Hi Nima,

First thanks for raising this issue here in the Forum.

I answer shortly here, as I explained the issue in detail on a shooted movie. The URL link of the movie is shared in this post.

 

  • firstly, LED No.4 blicking is NORMAL. most probably is it because of a factory setting to check the I/O module. since there was not any sensor connected it was blinking to alarm users: something is missing.
  • As immediate as you connect the sensor it won't blick anymore. As you also shot in your video. Same here on the video I did.
  • Sensors LEDs will blick for another scenario! if the sensor channels are not configured( By VampSet engineering tool of V321) but the sensor is connected physically to its channel. Then again to alarm users the related LED will blink.
  • Last but not least, I grab your attention to the fact that any kind of sensor configuration change( enabling, disabling ...) should be updated to the V321 central unit by the VampSet engineering tool.
  • In the movie you shared, I/o module itself & V321 central unit both are in a faulty condition. I mean wrench  LEDs are RED. the reason is you've not connected them together. It must be done by Schneider standard cable. The characteristics and ref. The numbers of these cables are available in our manuals.

To have a better understanding please take a moment to watch the video I shot. you may download it from below URL link, please.

Arc Applications & Solutions-Center of Excellence and Technology Leadership at Schneider Electric-Digital Power Connected Devices

See Answer In Context

Tags (1)
3 Replies 3
H_ERSHADZADEH
Lieutenant JG Lieutenant JG
Lieutenant JG
2
1030

Re: Arc Protection I/O unit error

Hi Nima,

First thanks for raising this issue here in the Forum.

I answer shortly here, as I explained the issue in detail on a shooted movie. The URL link of the movie is shared in this post.

 

  • firstly, LED No.4 blicking is NORMAL. most probably is it because of a factory setting to check the I/O module. since there was not any sensor connected it was blinking to alarm users: something is missing.
  • As immediate as you connect the sensor it won't blick anymore. As you also shot in your video. Same here on the video I did.
  • Sensors LEDs will blick for another scenario! if the sensor channels are not configured( By VampSet engineering tool of V321) but the sensor is connected physically to its channel. Then again to alarm users the related LED will blink.
  • Last but not least, I grab your attention to the fact that any kind of sensor configuration change( enabling, disabling ...) should be updated to the V321 central unit by the VampSet engineering tool.
  • In the movie you shared, I/o module itself & V321 central unit both are in a faulty condition. I mean wrench  LEDs are RED. the reason is you've not connected them together. It must be done by Schneider standard cable. The characteristics and ref. The numbers of these cables are available in our manuals.

To have a better understanding please take a moment to watch the video I shot. you may download it from below URL link, please.

Arc Applications & Solutions-Center of Excellence and Technology Leadership at Schneider Electric-Digital Power Connected Devices
Tags (1)
NiMo
Crewman
Crewman
1
1006

Re: Arc Protection I/O unit error

Hi Hamed

Thank you very much for your support and helpful remarks and video.

I tested accordingly, and now everything is ok.

 

Thanks again for your time on our problem. 

 

 

Tags (1)
H_ERSHADZADEH
Lieutenant JG Lieutenant JG
Lieutenant JG
0 Likes
0
994

Re: Arc Protection I/O unit error

@NiMo 

With pleasure! 

Keep it up Nima. & talk soon.

 

Regards,

Hamed

Arc Applications & Solutions-Center of Excellence and Technology Leadership at Schneider Electric-Digital Power Connected Devices