Selectivity between ComPacT NSX and EasyPact CVS
Hi, I would like to ask about the possibility to do selectivity with ComPacT NSX and EasyPact CVS, I´ve used Electrical Calculation Tools and I see that there are some compatibilities, attached a document. Please someone can confirm this information, and please share the selectivity tables between CVS and NSX...
In documents about coordination tables I didn´t find this compatibility
Thanks!
FYI @LarisaFranco
- Labels:
-
Power Distribution Software
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-08 03:58 AM . Last Modified: 2024-10-20 09:46 PM
Hi,
Thank you for your question.
From the marketing point of view, we do not promote the combination of this offers (as a selectivity table).
User may not be able to see this combination in the catalogue.
So, on the software tools, the selectivity between "CVS & NSX" and the vice versa is not allowed.
However, the CVS is more or less equivalent to similar rating NSX breaker.
So, as it is for the selectivity also. If you replace the equivalent NSX breaker in the place of CVS, you are expected to get the same selectivity value. By using this method, we can cross verify the authenticity of the selectivity result for CVS breakers.
I hope it clears your doubt.
If you have further query, feel free to ask.
Thanks,
Team - Ecodial Expert Support.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-08 03:58 AM . Last Modified: 2024-10-20 09:46 PM
Hi,
Thank you for your question.
From the marketing point of view, we do not promote the combination of this offers (as a selectivity table).
User may not be able to see this combination in the catalogue.
So, on the software tools, the selectivity between "CVS & NSX" and the vice versa is not allowed.
However, the CVS is more or less equivalent to similar rating NSX breaker.
So, as it is for the selectivity also. If you replace the equivalent NSX breaker in the place of CVS, you are expected to get the same selectivity value. By using this method, we can cross verify the authenticity of the selectivity result for CVS breakers.
I hope it clears your doubt.
If you have further query, feel free to ask.
Thanks,
Team - Ecodial Expert Support.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-17 08:08 PM
Hi
Can we consider selectivity CVS upstream and NSX dowstream, but not NSX upstream and CVS downstream?
Regarding management approval, do you mean local management?