Protection for Patient's Room (Hospital)

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Protection for Patient's Room (Hospital)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
80
J_Travostino
Sisko J_Travostino Sisko
70
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Expert on Demand for Standards & Regulations

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Start a Topic
Solved
HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2022-02-15 05:37 PM

1 Like
2
1408
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-15 05:37 PM

Protection for Patient's Room (Hospital)

I found this interesting question in 377698 and would like to be discuss by Experts in this forum please 🙏

 

I would like to ask, in the patient's room for leakage current protection is it enough with ELCB 10 ma or should use OT Panel if the patient's room stay there is active medical action activity such as pacemaker, intubation and others?

Labels
  • Labels:
  • Safety - People Safety
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
faisalamir
Lieutenant faisalamir Lieutenant
Lieutenant

Posted: ‎2022-02-15 07:41 PM . Last Modified: ‎2022-02-16 08:14 AM

2 Likes
1
1402
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-15 07:41 PM . Last Modified: ‎2022-02-16 08:14 AM

Hello @HelvinHermanT 

 

Refer to IEC 60634-7-710

 

Medical locations have been classified in 3 groups:

 

Group 0: Medical location where no medical electrical equipment is in contact with the body

 

Group 1: Medical location where medical electrical have to be used as follows: externally or invasively to any part of the body. A limited residual 30mA current device is mandatory

 

Group 2: Medical location where medical electrical equipment have to be used into the body. Isolated ground system is mandatory

 

I assume that room equipped with the medical equipment that needs to have used into the body directly shall categorize into group-2

 

Group-2 specify that the electrical system shall apply IT Network system/Ungrounded  

 

Hope this reference is help

 

Regards, 

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
faisalamir
Lieutenant faisalamir Lieutenant
Lieutenant

Posted: ‎2022-02-15 07:41 PM . Last Modified: ‎2022-02-16 08:14 AM

2 Likes
1
1403
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-15 07:41 PM . Last Modified: ‎2022-02-16 08:14 AM

Hello @HelvinHermanT 

 

Refer to IEC 60634-7-710

 

Medical locations have been classified in 3 groups:

 

Group 0: Medical location where no medical electrical equipment is in contact with the body

 

Group 1: Medical location where medical electrical have to be used as follows: externally or invasively to any part of the body. A limited residual 30mA current device is mandatory

 

Group 2: Medical location where medical electrical equipment have to be used into the body. Isolated ground system is mandatory

 

I assume that room equipped with the medical equipment that needs to have used into the body directly shall categorize into group-2

 

Group-2 specify that the electrical system shall apply IT Network system/Ungrounded  

 

Hope this reference is help

 

Regards, 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2022-02-16 05:42 PM . Last Modified: ‎2022-02-17 01:39 AM

In response to faisalamir
1 Like
0
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-16 05:42 PM . Last Modified: ‎2022-02-17 01:39 AM

Hi @faisalamir ,

 

Thank you for your respond.

 

Yes, IEC 60634-7-710 (Low-voltage electrical installations - Part 7-710: Requirements for special installations or locations - Medical locations) regulate about Installation in Medical location.

In Indonesia we also adopted this standard into SNI 0225-7-710:2020 (Persyaratan Umum Instalasi Listrik (PUIL) 2020 – Bagian 7-710: Persyaratan untuk instalasi atau lokasi khusus – Lokasi medis).

 

I agreed with you, if there are equipments used into the body then it should be classified as group 2.

You also mentioned IEC 60634-7-710 Group-2 required isolated ground system, so it will require OT Panel with Isolation Transformer inside.

 

 

Perhaps there are other opinions ?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.