Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-07-14 12:26 AM
Dear Experts! My customer would like to install Heattags into his LV distribution cabinets. He did not want to use any monitoring system. The only requirement is operate an alarm contact in case the high temperature or Heattag air quality alarm. < My first idea to use PowerTag Link to collect Heattag signals, but I don know how can I transfer the alarms to one relay contact.
Can I use an ACTI9 PowerTag C IO module for this task? It is possible to address those alarm signals to operate IO module?
Or can you offer me an other simple cheep solution to solve this request?
Thanks in advance
Janos
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-07-26 12:56 AM
hello @Janos_A
Did you have this document ?
I think and hope it answer to your question.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-07-26 12:56 AM
hello @Janos_A
Did you have this document ?
I think and hope it answer to your question.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-11-14 09:32 PM
Hi, Gregoire Brun, This Nagabhushana Schneider works for Schneider Secure power, I did not get any information to operate relay from Heattag, kind share some details ASAP
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-11-16 02:44 AM
Hello @Janos_A ,
Better use Panel Server as a gateway for your HeatTag. Panel Server offer native e-mail alarming feature.
With PowerTag Link, this is more complicated because you need to use your own SMTP server and I'm not sure that PowerTag Link still conform with Cipher Suites of many SMTP providers.
Regards,