Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-09-23 11:50 PM
Hello,
if there are any engineers in here, especially from Schneider, can some please settle and argument I had with my instructors today: I said that thermal overload and magnetic overcurrent are the protections within a CB, however they said it is thermal overcurrent and magnetic overload.
I said that overload is heat I.e. thermal caused by slower excessive current (motor stalls, high loads) that generates the excessive heat, whereas the magnetic overcurrent is for shortcut and/or high inrush currents caused by faults, shorts etc. My instructors argue that the opposite is in effect what happens.
What is it?
Kind regards,
Dave
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-10-02 01:47 AM
Hello @Dave47,
I will try to make it simple as possible and take the example of Miniature Circuit Breaker (this is a bit different for industrial circuit breakers).
A MCB has 2 kind of protections:
Let's take a 16 Amps C curve MCB:
Thermal protection is dedicated to small overcurrents (cable heat up):
Magnetic protection is dedicated to high overcurrents :
This is more a story of current quantity / variation inside your circuit breaker. For me overcurrent and overload are similar.
Regards,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-10-02 01:47 AM
Hello @Dave47,
I will try to make it simple as possible and take the example of Miniature Circuit Breaker (this is a bit different for industrial circuit breakers).
A MCB has 2 kind of protections:
Let's take a 16 Amps C curve MCB:
Thermal protection is dedicated to small overcurrents (cable heat up):
Magnetic protection is dedicated to high overcurrents :
This is more a story of current quantity / variation inside your circuit breaker. For me overcurrent and overload are similar.
Regards,
Link copied. Please paste this link to share this article on your social media post.