NSX PowerTag

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • NSX PowerTag
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
80
J_Travostino
Sisko J_Travostino Sisko
70
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Expert on Demand for Standards & Regulations

Related Products
product field
Schneider Electric
ComPacT NSX, new generation

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Start a Topic
Solved
Peter_Hall
Lt. Commander | EcoXpert Master Peter_Hall Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master

Posted: ‎2023-01-28 05:44 AM

0 Likes
5
3269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-28 05:44 AM

NSX PowerTag

In the past we have used a concentrator to collect NSX PowerTag information. Now we understand that this can be done by using a Panel Sever. However, how do we give our customers local visibility on the panel? it used to be done by adding an FDM128 to the system which would pick up from the concentrators fitted within the switchboard. To get information on the panel servers in the UK is not the easiest task!

 

In the past we would fit a concentrator to each cable way to connect to PowerTags in the columns that feed into that cable way. Is there a replacement for the concentrator? i cannot think that we would need to use multiple Panel Servers? Any recommendations as to how many columns of outgoing NSX MCCB's the new Panel Servers can connect to?

Labels
  • Labels:
  • Connectivity
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
RHH
Commander | EcoXpert Master RHH Commander | EcoXpert Master
Commander | EcoXpert Master

Posted: ‎2023-01-28 02:23 PM . Last Modified: ‎2023-01-28 02:38 PM

0 Likes
1
3257
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-28 02:23 PM . Last Modified: ‎2023-01-28 02:38 PM

Yes, the panel server by itself is a concentrator as well. Looking at the PAS600 and PAS800, but to get both local and ‘cloud’ we used micrologic E instead of the PowerTags and wire that out with an panel server/concentrator and FDM. P.s. I believe we used something else instead of the panel servers because yes they are quite expensive. But with our setup we could get max. 8 per concentrator, I don’t remember if that was the max usage of the FDM12(8) or the max usage of the concentrator though. Maybe both.


In the product page I added to this reply you can see both panel server and meter (display) connected. I hope this is what you meant, otherwise I would gladly hear it and try to be of assistance in another way.

 


Kind regards,

Rick

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Szymon_Hochół
Captain Szymon_Hochół Captain
Captain

Posted: ‎2023-01-31 05:20 AM

In response to Peter_Hall
0 Likes
0
3192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-31 05:20 AM

Hi @Peter_Hall ,

Smartlink SI-D (A9XMWA20) is already discontinued and was replaced by PowerTag Link (A9XMWD20):

1.JPG

PowerTag Link is also reaching end of its life and the device to replace it is EcoStruxure Panel Server (PAS):

2.JPG

The most 1:1 replacement of SI-D and PTag Link is Panel Server Entry(PAS400) - it has exactly the same form factor, power supply and also 1 ETH port:

3.JPG

The thing is - it is not launched yet, will be available mid-2023. So if you're looking for a replacement today, the best fit is Panel Server Universal (PAS600). It is slightly wider, but in exchange offers dual ETH ports to make you wiring easier:

4.JPG

Also, please note that all Panel Server models have WiFi feature - so wiring might not be needed at all.

 

Cheers

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
RHH
Commander | EcoXpert Master RHH Commander | EcoXpert Master
Commander | EcoXpert Master

Posted: ‎2023-01-28 02:23 PM . Last Modified: ‎2023-01-28 02:38 PM

0 Likes
1
3258
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-28 02:23 PM . Last Modified: ‎2023-01-28 02:38 PM

Yes, the panel server by itself is a concentrator as well. Looking at the PAS600 and PAS800, but to get both local and ‘cloud’ we used micrologic E instead of the PowerTags and wire that out with an panel server/concentrator and FDM. P.s. I believe we used something else instead of the panel servers because yes they are quite expensive. But with our setup we could get max. 8 per concentrator, I don’t remember if that was the max usage of the FDM12(8) or the max usage of the concentrator though. Maybe both.


In the product page I added to this reply you can see both panel server and meter (display) connected. I hope this is what you meant, otherwise I would gladly hear it and try to be of assistance in another way.

 


Kind regards,

Rick
Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Peter_Hall
Lt. Commander | EcoXpert Master Peter_Hall Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master

Posted: ‎2023-01-29 02:09 AM

In response to RHH
0 Likes
0
3248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-29 02:09 AM

Hi Rick,

Thank you for your reply. When we used the concentrator in the past with the FDM128 each concentrator became a landing page 'tile' therefore we had as you say 8 tiles/concentrators. When we opened each tile we found 20 devices connected. Therefore in theory it would be possible to connect 8 x concentrators x 20 devices (older type concentrators) = 160 devices.... A useful tool. However, from what i am seeing this morning i think that the new offer of panel server is clearly aimed at the BMS/Cloud connection with NSX 'E' trip units being used for applications that require local indication. An opportunity missed? All that was needed was two Ethernet ports on both the concentrators and the FDM128 and you had almost the perfect setup....

Reply

Link copied. Please paste this link to share this article on your social media post.

Szymon_Hochół
Captain Szymon_Hochół Captain
Captain

Posted: ‎2023-01-30 03:26 AM . Last Modified: ‎2023-01-30 03:28 AM

0 Likes
2
3213
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-30 03:26 AM . Last Modified: ‎2023-01-30 03:28 AM

Hi @Peter_Hall ,

first, could you please confirm what "concentrator" you used in the past? Was it PowerTag Link?

I confirm that indeed, Panel Server is the replacement for variety of legacy communication devices, including PowerTag Link for wireless. PAS600 is the way to go today, and later this year a PAS400 will be launched to provide more cost-effective, yet wireless-only option.

 

Back to your question, PAS600 does support PowerTag NSX and it does support FDM128. All the information is to be found in FDM128 User Manual:

 

Przechwytywanie.JPG

You can also refer to Panel Server User Manual and Release Notes.

Finally, there is a dedicated forum section for the gateways. This is the best place to ask questions about these devices, as it is regularly visited by product experts.

 

Hope this helps.

 

Regards

Reply

Link copied. Please paste this link to share this article on your social media post.

Peter_Hall
Lt. Commander | EcoXpert Master Peter_Hall Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master

Posted: ‎2023-01-30 08:47 AM

In response to Szymon_Hochół
0 Likes
1
3200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-30 08:47 AM

Hi Szymon,

Thank you for your reply. In the past we have fitted Smartlink SI-D units to the cableways and connected to the NSX PowerTag units. We then connected the FDM128 to the SI-D units via TCP/IP and connected to our customers network directly or used a Com'X 210 and split the ports.

I understand the connection to the FDM128 and to the customers network via the Panel Server. Is there a replacement for SI-D units which we would fit into each outgoing cable way?

Point noted in regards to positing on the Gateway specific forum.

Unfortunately information on these replacement devices is a little vague in the UK at the moment.

 

Best regards,

Peter Hall.

Reply

Link copied. Please paste this link to share this article on your social media post.

Szymon_Hochół
Captain Szymon_Hochół Captain
Captain

Posted: ‎2023-01-31 05:20 AM

In response to Peter_Hall
0 Likes
0
3193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-31 05:20 AM

Hi @Peter_Hall ,

Smartlink SI-D (A9XMWA20) is already discontinued and was replaced by PowerTag Link (A9XMWD20):

1.JPG

PowerTag Link is also reaching end of its life and the device to replace it is EcoStruxure Panel Server (PAS):

2.JPG

The most 1:1 replacement of SI-D and PTag Link is Panel Server Entry(PAS400) - it has exactly the same form factor, power supply and also 1 ETH port:

3.JPG

The thing is - it is not launched yet, will be available mid-2023. So if you're looking for a replacement today, the best fit is Panel Server Universal (PAS600). It is slightly wider, but in exchange offers dual ETH ports to make you wiring easier:

4.JPG

Also, please note that all Panel Server models have WiFi feature - so wiring might not be needed at all.

 

Cheers

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore