Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-25 12:38 AM
Hi
Does any one useing the new power commition 2.35 to disable maintainance alarm, but only 3 month maintainace alarm can't be disable. 1 month and 6 month maintainace alarm can be disable.
Anyone has happened this problem before?
Many thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-16 04:58 AM
Hi @Ray_Chang_EPEC ,
Wish you are very well.
It seems that from version V2.33 the "Schedule Manufacturer Maintenance within three months" is not configurable anymore, it only accepts enable. This was the answer of Expert Technical Support of EPC for a similar case we had.
Sorry.
Best Regards,
Neide
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-25 07:00 AM
Hello @Ray_Chang_EPEC, thank you for your post, we'll come back to you!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-14 08:58 PM
Hi @Manon_Chaboud :
Sorry for the bother, is there any futher information about this problem?
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-16 04:58 AM
Hi @Ray_Chang_EPEC ,
Wish you are very well.
It seems that from version V2.33 the "Schedule Manufacturer Maintenance within three months" is not configurable anymore, it only accepts enable. This was the answer of Expert Technical Support of EPC for a similar case we had.
Sorry.
Best Regards,
Neide
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-19 06:30 PM
Hi @NeiB
Thanks for the reply.
Just wnat to make sure. Cause this three month is not on our control when to start. (I think it's count on oprate time from MTZ itself) So we have to make sure customer understand that every three month MTZ will alarm for maintainance. And it's not able to disable. Can you help on clarify this? Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-04 09:22 PM . Last Modified: 2025-06-04 09:23 PM
Hi @Ray_Chang_EPEC
The name of the alarm is "Schedule Manufacturer Maintenance within three months."
Manufacturer maintenance alarm triggered based on the configuration of "Environmental condition" & "application criticality."
After the said 5 years/3 years/2 years, user has to complete the "Schedule Manufacturer Maintenance within three months
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-04 10:54 PM
Hi @Jibin_SAM :
Thanks for the reply.
Dose the "Environmental condition" & "application criticality." is self detect By MTZ?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.