MCC IT Network 525V/690V
  • Power Distribution IEC
  • MCC IT Network 525V/690V
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
80
J_Travostino
Sisko J_Travostino Sisko
70
Posted: ‎2020-05-04 06:37 AM . Last Modified: ‎2020-11-20 07:59 AM
1849
I`m looking for a solution of MCC Panel to be used in IT Network with 525V or 690V.
The combination contactor + breaker needs to achieve 65kA or more.
Could you share your thoughts about that?
  • Power Availability
  • Products
MathieuGuillot
Lieutenant MathieuGuillot Lieutenant
Lieutenant
Posted: ‎2020-05-05 12:20 AM . Last Modified: ‎2020-11-20 07:58 AM
The ability of a circuit breaker to operate in IT earthing system is covered by the normative Annex H of IEC/EN 60947-2.
All our product TeSys GV and ComPact NSX are compliant to this Annex H for all operating voltages (if not they would be marked with a strikethrough IT).  Compact NSX HB1 for instance is suitable for 690V 65kA  IT application. (They are used often in 690V Marine application that is 100% IT for instance)
For Contactor there is no special requirement according to earthing system. Circuit-breaker & Contactor coordination tests according to IEC/EN 60947-4-1 are as well not depending of earthing system.
Some additional requirment may exist in some countries. Do you have some special requirments in addition to compliance with IEC/EN 60947-2 and IEC/EN 60947-4-1 in your project ?
Regards
MathieuGuillot
Lieutenant
Regards