Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-02-03 05:36 AM . Last Modified: 2022-02-03 06:33 AM
What is the Impact of Electric Vehicle Charging to Power Factor of the Electrical Installation ?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-02-09 07:46 AM . Last Modified: 2022-02-09 08:36 AM
Hello @HelvinHermanT
If it's an AC charger, the impact should rather be on the EV side (the car), not the EVSE (charger). The cos Phi generator is on the EVSE side for DC chargers.
Then, it would depend on the EV model, but we can estimate Power Factor between 0.8 and 1, with a typical current distortion rate is around 20%.
If you are interested, we can obtain an extract from the standards for cars where the limits are set regarding current distortion.
Thanks,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-02-10 07:45 AM
For AC charging stations, 99% of the current consumed is that consumed directly by the vehicle. In this case, the harmonic limits are defined by IEC 61851-21-1 §5.3.2 which is specific to on-board vehicle chargers. In particular (see picture)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-02-03 05:54 AM . Last Modified: 2022-02-03 05:57 AM
Hello Helvin,
I don't think it influences much anymore in our regions due to EU regulations regarding PFC (Power Factor Correction). I suppose more and more units which adjust/toxicate the power factor are supplied with this tech due to these regulations.
I guess/bet this is also the case with the verhicle charging industry?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-02-09 07:46 AM . Last Modified: 2022-02-09 08:36 AM
Hello @HelvinHermanT
If it's an AC charger, the impact should rather be on the EV side (the car), not the EVSE (charger). The cos Phi generator is on the EVSE side for DC chargers.
Then, it would depend on the EV model, but we can estimate Power Factor between 0.8 and 1, with a typical current distortion rate is around 20%.
If you are interested, we can obtain an extract from the standards for cars where the limits are set regarding current distortion.
Thanks,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-02-10 07:45 AM
For AC charging stations, 99% of the current consumed is that consumed directly by the vehicle. In this case, the harmonic limits are defined by IEC 61851-21-1 §5.3.2 which is specific to on-board vehicle chargers. In particular (see picture)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-02-04 03:00 AM
Hi, How would this be impacted in the case of a DC Charger and how would the input current be impacted? Say we start with the 90% Charger Efficienty
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.