Impact of Electric Vehicle Charging to Power Factor

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Impact of Electric Vehicle Charging to Power Factor
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
80
J_Travostino
Sisko J_Travostino Sisko
70
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Expert on Demand for Standards & Regulations

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Start a Topic
Solved
HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2022-02-03 05:36 AM . Last Modified: ‎2022-02-03 06:33 AM

0 Likes
4
10121
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-03 05:36 AM . Last Modified: ‎2022-02-03 06:33 AM

Impact of Electric Vehicle Charging to Power Factor

What is the Impact of Electric Vehicle Charging to Power Factor of the Electrical Installation ?

 

Labels
  • Labels:
  • eMobility
  • Energy management
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
victorarce
Ensign victorarce Ensign
Ensign

Posted: ‎2022-02-09 07:46 AM . Last Modified: ‎2022-02-09 08:36 AM

3 Likes
1
10068
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-09 07:46 AM . Last Modified: ‎2022-02-09 08:36 AM

Hello @HelvinHermanT 

 

If it's an AC charger, the impact should rather be on the EV side (the car), not the EVSE (charger). The cos Phi generator is on the EVSE side for DC chargers.

 

Then, it would depend on the EV model, but we can estimate Power Factor between 0.8 and 1, with a typical current distortion rate is around 20%.


If you are interested, we can obtain an extract from the standards for cars where the limits are set regarding current distortion.

 

Thanks,

Driving towards a 100% electric mobility and net-zero destination

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

victorarce
Ensign victorarce Ensign
Ensign

Posted: ‎2022-02-10 07:45 AM

In response to victorarce
3 Likes
0
10057
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-10 07:45 AM

For AC charging stations, 99% of the current consumed is that consumed directly by the vehicle. In this case, the harmonic limits are defined by IEC 61851-21-1 §5.3.2 which is specific to on-board vehicle chargers. In particular (see picture)harmonics.png

Driving towards a 100% electric mobility and net-zero destination

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
RHH
Commander | EcoXpert Master RHH Commander | EcoXpert Master
Commander | EcoXpert Master

Posted: ‎2022-02-03 05:54 AM . Last Modified: ‎2022-02-03 05:57 AM

2 Likes
0
10111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-03 05:54 AM . Last Modified: ‎2022-02-03 05:57 AM

Hello Helvin,

 

I don't think it influences much anymore in our regions due to EU regulations regarding PFC (Power Factor Correction). I suppose more and more units which adjust/toxicate the power factor are supplied with this tech due to these regulations.

I guess/bet this is also the case with the verhicle charging industry?




Kind regards,

Rick
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

victorarce
Ensign victorarce Ensign
Ensign

Posted: ‎2022-02-09 07:46 AM . Last Modified: ‎2022-02-09 08:36 AM

3 Likes
1
10069
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-09 07:46 AM . Last Modified: ‎2022-02-09 08:36 AM

Hello @HelvinHermanT 

 

If it's an AC charger, the impact should rather be on the EV side (the car), not the EVSE (charger). The cos Phi generator is on the EVSE side for DC chargers.

 

Then, it would depend on the EV model, but we can estimate Power Factor between 0.8 and 1, with a typical current distortion rate is around 20%.


If you are interested, we can obtain an extract from the standards for cars where the limits are set regarding current distortion.

 

Thanks,

Driving towards a 100% electric mobility and net-zero destination
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

victorarce
Ensign victorarce Ensign
Ensign

Posted: ‎2022-02-10 07:45 AM

In response to victorarce
3 Likes
0
10058
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-10 07:45 AM

For AC charging stations, 99% of the current consumed is that consumed directly by the vehicle. In this case, the harmonic limits are defined by IEC 61851-21-1 §5.3.2 which is specific to on-board vehicle chargers. In particular (see picture)harmonics.png

Driving towards a 100% electric mobility and net-zero destination
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

vikasprawal
vikasprawal
Cadet

Posted: ‎2024-02-04 03:00 AM

0 Likes
0
5407
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-04 03:00 AM

Hi, How would this be impacted in the case of a DC Charger and how would the input current be impacted? Say we start with the 90% Charger Efficienty 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore