Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

Close
Important Announcement: WELCOME to the Schneider Electric Community! We have moved to a new address: community.se.com — bookmark it today and contact SchneiderCommunity.Support@se.com if you have any questions!
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82755members
350542posts

Impact of Electric Vehicle Charging to Power Factor

Power Distribution and Digital

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Solved
HelvinHermanT
Captain Captain
Captain
0 Likes
3
903

Impact of Electric Vehicle Charging to Power Factor

What is the Impact of Electric Vehicle Charging to Power Factor of the Electrical Installation ?

 

Tags (1)

Accepted Solutions
victorarce
Ensign Ensign
Ensign

Re: Impact of Electric Vehicle Charging to Power Factor

Hello @HelvinHermanT 

 

If it's an AC charger, the impact should rather be on the EV side (the car), not the EVSE (charger). The cos Phi generator is on the EVSE side for DC chargers.

 

Then, it would depend on the EV model, but we can estimate Power Factor between 0.8 and 1, with a typical current distortion rate is around 20%.


If you are interested, we can obtain an extract from the standards for cars where the limits are set regarding current distortion.

 

Thanks,

Driving towards a 100% electric mobility and net-zero destination

See Answer In Context

Tags (1)
victorarce
Ensign Ensign
Ensign

Re: Impact of Electric Vehicle Charging to Power Factor

For AC charging stations, 99% of the current consumed is that consumed directly by the vehicle. In this case, the harmonic limits are defined by IEC 61851-21-1 §5.3.2 which is specific to on-board vehicle chargers. In particular (see picture)harmonics.png

Driving towards a 100% electric mobility and net-zero destination

See Answer In Context

Tags (1)
3 Replies 3
RHH-Eltechna
Commander | EcoXpert Master Commander | EcoXpert Master
Commander | EcoXpert Master

Re: Impact of Electric Vehicle Charging to Power Factor

Hello Helvin,

 

I don't think it influences much anymore in our regions due to EU regulations regarding PFC (Power Factor Correction). I suppose more and more units which adjust/toxicate the power factor are supplied with this tech due to these regulations.

I guess/bet this is also the case with the verhicle charging industry?




Kind regards,

Rick - Eltechna B.V.
signature-RHHH
Tags (1)
victorarce
Ensign Ensign
Ensign

Re: Impact of Electric Vehicle Charging to Power Factor

Hello @HelvinHermanT 

 

If it's an AC charger, the impact should rather be on the EV side (the car), not the EVSE (charger). The cos Phi generator is on the EVSE side for DC chargers.

 

Then, it would depend on the EV model, but we can estimate Power Factor between 0.8 and 1, with a typical current distortion rate is around 20%.


If you are interested, we can obtain an extract from the standards for cars where the limits are set regarding current distortion.

 

Thanks,

Driving towards a 100% electric mobility and net-zero destination
Tags (1)
victorarce
Ensign Ensign
Ensign

Re: Impact of Electric Vehicle Charging to Power Factor

For AC charging stations, 99% of the current consumed is that consumed directly by the vehicle. In this case, the harmonic limits are defined by IEC 61851-21-1 §5.3.2 which is specific to on-board vehicle chargers. In particular (see picture)harmonics.png

Driving towards a 100% electric mobility and net-zero destination
Tags (1)