[IEC 61439 for LV equipment April 16th 2020 webinar] - Specifications
Question from Georgios Andreadis:
So, we have the right to request verification tests of our specified assembly from the panel builder for every project, before site installation?
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-04-21 09:10 AM
Hello,
If the assembly manufacturer used a system from an original manufcaturer and respect the rules from his documentation he would not have to perform additional test.
If there are some deviation(s) based on the comparison between the certification and the assembly to deliver yes additional tests can be performed.
Pascal Lepretre
Sytandardization Officer - Edison Expert
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-04-21 09:10 AM
Hello,
If the assembly manufacturer used a system from an original manufcaturer and respect the rules from his documentation he would not have to perform additional test.
If there are some deviation(s) based on the comparison between the certification and the assembly to deliver yes additional tests can be performed.
Pascal Lepretre
Sytandardization Officer - Edison Expert