How to design a low voltage distribution board?

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • How to design a low voltage distribution board?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
80
J_Travostino
Sisko J_Travostino Sisko
70
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Expert on Demand for Standards & Regulations

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Power Distribution and Digital Support
Start a Topic
Manon_Chaboud
Commander Manon_Chaboud Commander
Commander

Posted: ‎2025-07-24 02:06 AM . Last Modified: ‎2025-07-24 02:08 AM

2 Likes
0
830
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-24 02:06 AM . Last Modified: ‎2025-07-24 02:08 AM

How to design a low voltage distribution board?

Designing a low voltage distribution board (LVDB) involves careful planning to ensure safety, reliability, and compliance with electrical standards.

You can find here a step-by-step guide to help you through the process.

 

Step 1: Define the requirements

  • Determine the voltage level (e.g., 230V single-phase or 400V three-phase).
  • Identify the types of loads (lighting, sockets, HVAC, motors, etc.).
  • Calculate the total power demand (in kW or kVA).
  • Decide on the number of circuits needed.

Step 2: Choose the enclosure

  • Select the material (metal or plastic).
  • Choose the IP rating based on the environment (e.g., IP65 for outdoor).
  • Ensure the size allows for all components and future expansion.

Step 3: Select the components

  • Main Incomer: MCCB or MCB with suitable rating.
  • Busbars: rated for total current.
  • Outgoing MCBs: one for each circuit, sized to the load.
  • RCDs/RCBOs: for earth leakage protection.
  • Surge Protection Device (SPD): optional but recommended.
  • Neutral and Earth Bars: for proper termination.

Step 4: Perform load calculations

  • Apply diversity factors to avoid oversizing.
  • Ensure the sum of outgoing breakers does not exceed the main breaker rating.

Step 5: Design the wiring and layout

  • Create a Single-Line Diagram (SLD) showing all connections.
  • Size the cables based on current, voltage drop, and installation conditions.
  • Clearly label all breakers and terminals.

Step 6: Ensure compliance with standards

  • Follow local regulations (e.g., IEC 61439, NF C 15-100 in France).
  • Ensure proper earthing and bonding.
  • Prepare documentation for inspection and maintenance.

Step 7: Testing and commissioning

  • Perform:
    • Insulation resistance test
    • Continuity of protective conductors
    • Polarity check
    • Functional testing of RCDs and breakers

 

In conclusion, a well-designed LV distribution board ensures safe, efficient, and compliant power distribution. Follow each step carefully to meet both technical and regulatory requirements.

Labels
  • Labels:
  • How to
  • Knowledge
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore