Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-01-26 07:03 AM . Last Modified: 2022-01-26 07:08 AM
According to Ground Fault Protection Low voltage expert guides n° 2 https://download.schneider-electric.com/files?p_enDocType=Technical+leaflet&p_File_Name=DBTP140GUI_E...
I would like to install ground fault detection for our system to comply with 4.1.1.2 Study 2 Diagram 2.
Ground fault detected by using 2 Source Ground Return (SGR) for 2 source , one ground connection. PEN.
Power system configuration is 3 phase 4 wires. ACB 3 poles MTZ, NW PEN.
There are three ACBs which are ACB incoming#1, ACB incoming#2 and ACB bus-tie.
Our interested component is
Micrologic 6.0E
ZCT = LV833579SP
MDGF = LV848891SP
in this document, there is the recommended wiring diagram for case only 1 source vs 1 SGR.
No recommended wiring for 2 source vs 2 SGR. 4.1.1.2 Study 2 Diagram 2
I need help to recommend how to connect ZCT, MDGF and ACB status contact diagram to achieve 4.1.1.2 Study2 Diagram2.
I attach 2 solutions for your consider. however, if both are wrong, please suggest me. Thank you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-01-27 03:58 AM . Last Modified: 2022-01-28 02:07 AM
Hi @Golfdance,
For this case, you need to wire your GF system as per your solution 1. To size your switch, the LV833579SP Iron CT has a ratio of 1000:1.
Best regards
Patrick
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-01-27 03:58 AM . Last Modified: 2022-01-28 02:07 AM
Hi @Golfdance,
For this case, you need to wire your GF system as per your solution 1. To size your switch, the LV833579SP Iron CT has a ratio of 1000:1.
Best regards
Patrick