Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Search in
Posted: 2020-11-23 06:21 AM . Last Modified: 2024-11-22 04:25 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-11-23 06:21 AM . Last Modified: 2024-11-22 04:25 AM
I am working on a Commercial Complex project. I want to know how I can optimize the cost while selecting the equipment for my project in Ecodial?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-11-23 06:38 PM . Last Modified: 2020-11-23 06:41 PM
Thanks for your query on this subject of “finding an economical solution”
Introduction :
This can be achieved during the ‘electrical network design’ with the help of the ‘selection of protection devices’ by considering the coordination called ‘Cascading.’
This is specific property between the “Schneider Electric” protection devices. This is lab tested and tabulated.
Principle :
Cascading between two circuit breakers is achieved by using the tripping of the upstream circuit breaker (A) to help the downstream (load side) circuit breaker (B) to break the current. This allows the selection of downstream devices with lower breaking capacities, and therefore lower cost.
In other words, the upstream circuit breaker helps downstream devices break short circuit currents that are greater than the highest short circuit currents that they can break.
This can be explained from the following example(s);
Example 01:
In the following example The network design “without cascading” leads to the selection of “circuit breakers with high breaking capacities.”
* Icc = the prospective short circuit current
Example 2 :
Whereas in the following example;
The network design “with cascading” leads to the selection of “circuit breakers with less breaking capacities at the feeder level.”
This is how the cost of the project is saved by considering the ‘Cascading property between the circuit breakers’.
* Icu = The ultimate short circuit ‘breaking capacity’ of the ‘circuit breaker.’
* Icu reinforced = The enhanced ‘breaking capacity’ received due to the ‘cascading effect’ of the upstream circuit breaker.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-11-23 06:38 PM . Last Modified: 2020-11-23 06:41 PM
Thanks for your query on this subject of “finding an economical solution”
Introduction :
This can be achieved during the ‘electrical network design’ with the help of the ‘selection of protection devices’ by considering the coordination called ‘Cascading.’
This is specific property between the “Schneider Electric” protection devices. This is lab tested and tabulated.
Principle :
Cascading between two circuit breakers is achieved by using the tripping of the upstream circuit breaker (A) to help the downstream (load side) circuit breaker (B) to break the current. This allows the selection of downstream devices with lower breaking capacities, and therefore lower cost.
In other words, the upstream circuit breaker helps downstream devices break short circuit currents that are greater than the highest short circuit currents that they can break.
This can be explained from the following example(s);
Example 01:
In the following example The network design “without cascading” leads to the selection of “circuit breakers with high breaking capacities.”
* Icc = the prospective short circuit current
Example 2 :
Whereas in the following example;
The network design “with cascading” leads to the selection of “circuit breakers with less breaking capacities at the feeder level.”
This is how the cost of the project is saved by considering the ‘Cascading property between the circuit breakers’.
* Icu = The ultimate short circuit ‘breaking capacity’ of the ‘circuit breaker.’
* Icu reinforced = The enhanced ‘breaking capacity’ received due to the ‘cascading effect’ of the upstream circuit breaker.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.