Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Evolution in IEC61439-1/2

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Evolution in IEC61439-1/2
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
80
J_Travostino
Sisko J_Travostino Sisko
70
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Expert on Demand for Standards & Regulations

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2020-05-19 10:33 PM . Last Modified: ‎2021-10-27 11:03 AM

1 Like
4
2953
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-19 10:33 PM . Last Modified: ‎2021-10-27 11:03 AM

Evolution in IEC61439-1/2

Are you aware about the recent revision in IEC61439-1 ?

Do you know about the technical changes that are being incorporated in the latest edition?

Does it have significant impact on the existing range of offers?

 

Do post your queries / visit this forum for further details on the latest edition of IEC61439-1

 

Regards

S.Saravaanan

Principle Technical Expert

Labels
  • Labels:
  • Power Standards & Regulations
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2020-05-20 12:32 AM

In response to Anonymous user
1 Like
2
2946
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-20 12:32 AM

The IEC61439-1; edition 3 was published in the begining of May 2020. This third edition cancels and replaces the second edition which was published in 2011. There are few significant technical changes in included in thelatest edition namely:

 

1. Integration of electronic systems such as VFD, SMPS, UPD etc..although these electronic components are tested to their

    respective products standard, but when they are incorporated in assemblies the incorporation should be in accordance with

    the IEC 61439 series.

 

2. New terminology - Group rated Current of circuit & more emphasis on temperature rise verification on this characteristics.

 

3. Recognition of Aluminium as conductor with very well defined temperature rise criteria limits - 55K for Untreated Aluminium 

     to aluminium Joints

 

4. Increase in the test duration from 5 second to 60 second in case of Dielectric verification for the power frequency test.

 

5. Addition of requirements in respect of DC

 

6. Introduction of the concept of class I and class II assemblies regarding protection against electric shock.

 

There will be no significant impact on the existing solutions that are complying to edition 2 except on the temperature rise criteria's for Aluminium conductor. An rise of 55k on Al-Al joint is adapted so as to ensure safety & performance of the solution over a prolonged duration of service.

 

This is because, the Al-Al joints readily oxidizes and result in formation of strong insulating oxide layer which hinders the transfer of electrons resulting into thermal avalanche and subsequent thermal failure. Hence the criteria limit is set at 55K for an Al-Al joint in order to over come the above said problem.

 

Hope we have addressed your queries. Do revert back in case of any clarifications.

 

Regards

S.Saravanan

Principle Technical Expert

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2020-05-19 10:58 PM

0 Likes
3
2949
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-19 10:58 PM

Dear Expert

Can you explain in brief about the technical change in the revised standard.

Is there any impact in the design because of this evolution? If so what are the impacts in design / testing?

 

Thanks You

Regards

Magma Switchgears

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-05-20 12:32 AM

In response to Anonymous user
1 Like
2
2947
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-20 12:32 AM

The IEC61439-1; edition 3 was published in the begining of May 2020. This third edition cancels and replaces the second edition which was published in 2011. There are few significant technical changes in included in thelatest edition namely:

 

1. Integration of electronic systems such as VFD, SMPS, UPD etc..although these electronic components are tested to their

    respective products standard, but when they are incorporated in assemblies the incorporation should be in accordance with

    the IEC 61439 series.

 

2. New terminology - Group rated Current of circuit & more emphasis on temperature rise verification on this characteristics.

 

3. Recognition of Aluminium as conductor with very well defined temperature rise criteria limits - 55K for Untreated Aluminium 

     to aluminium Joints

 

4. Increase in the test duration from 5 second to 60 second in case of Dielectric verification for the power frequency test.

 

5. Addition of requirements in respect of DC

 

6. Introduction of the concept of class I and class II assemblies regarding protection against electric shock.

 

There will be no significant impact on the existing solutions that are complying to edition 2 except on the temperature rise criteria's for Aluminium conductor. An rise of 55k on Al-Al joint is adapted so as to ensure safety & performance of the solution over a prolonged duration of service.

 

This is because, the Al-Al joints readily oxidizes and result in formation of strong insulating oxide layer which hinders the transfer of electrons resulting into thermal avalanche and subsequent thermal failure. Hence the criteria limit is set at 55K for an Al-Al joint in order to over come the above said problem.

 

Hope we have addressed your queries. Do revert back in case of any clarifications.

 

Regards

S.Saravanan

Principle Technical Expert

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-06-02 02:27 AM

In response to Anonymous user
0 Likes
1
2876
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-02 02:27 AM

Dear Expert

 

Thank you for your prompt reply on the posted query.

 

As a system integrator/panel builder, can I replace / substitute a device with a similar device from another series from the same manufacturer. Also is it allowed to substitute the device from a different device manufacturer to that used in the original verification. I will be obliged if you could elaborate on this subject.

 

Thank You

Regards

Magma Switchgear

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-06-02 09:25 PM

In response to Anonymous user
0 Likes
0
2872
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-02 09:25 PM

Device substitution is dealt positively in IEC61439-1. As a manufacturer/system assembler, one has to be vigilant in substituting the device so as to ensure satisfactory thermal & short circuit performances.

 

Device substitution is allowed for functional units whose rated current doesn't exceed 1600A. 

 

In respect of temperature-rise, there are very strict design rules that permit the substitution of a device with a similar device from another series or even another make, without retesting. In this case, in addition to the physical arrangement being essentially the same, the power loss and terminal temperature-rise of the substitute device, when it is tested in accordance with its own product standard, should not be higher than those of the original device.

 

  1. The physical arrangement within the functional unit shall be maintained.
  2. The rating of a functional unit shall not be increased.
  3. The physical arrangements shall include terminal shields, conductor type, material, and connection sizes, mounting orientation, clearances to other parts, ventilation arrangements and terminal arrangement.
  4. The performance data on terminal temperatures and power loss may be obtained from the device manufacturer or from comparison tests undertaken by those responsible for the substitution.

 

For  short circuit performance, the substitution device should have a lower cut-off and energy limiting characteristics than that of the verified device. 

 

If both the above parameters are satisfactorily met, then device substitution is allowed as per IEC61439-1.

 

Hope I have clarified your doubts on device substitution. 

Do revert back for any queries.

 

Thank You

Regards

S.Saravanan

Principal Technical Expert

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore