Briefly Elaborate the difference between the old standards IEC 60439 and new standard IEC 61439?

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Briefly Elaborate the difference between the old standards IEC 60439 and new standard IEC 61439?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
80
J_Travostino
Sisko J_Travostino Sisko
70
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Expert on Demand for Standards & Regulations

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2020-05-20 02:16 AM . Last Modified: ‎2021-10-27 11:03 AM

1 Like
1
3086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-20 02:16 AM . Last Modified: ‎2021-10-27 11:03 AM

Briefly Elaborate the difference between the old standards IEC 60439 and new standard IEC 61439?

P;ease guide how the new standard IEC 61439 different from IEC 60439 in terms of safety features of the Panel?

Labels
  • Labels:
  • Power Standards & Regulations
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2020-05-25 09:57 PM

1 Like
0
3053
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-25 09:57 PM

Its now more than 10+ years since the launch of IEC61439 series.The following aspects are addressed more effectively in IEC61439 when compared to its predecessor IEC60439:

 

  1. The number of mechanical operating cycles for main contacts and other parts has been increased to 200.
  2. For thermal evaluation - Verification by calculation is limited to a 630A for single compartments & upto 1600A for multiple compartments.
  3. The rated diversity factor is more clearly described, with each circuit requiring a defined rating.
  4. Neutral cross section is raised to a minimum of 50% of phase cross section, valid for PEN conductors too.
  5. Clearance verification by design may be applied utilizing a ‘safety factor’ of 50%.
  6. Shared responsibility between Original Manufacturer vs. ASSEMBLY Manufacturer.
  7. Agreements between Customer and Manufacturer are more detailed and extended.
  8. Concept of Type Testing & Partially Type Testing are replaced by Design Verification.
  9. Routine Tests are replaced by Routine Verification.
  10. Design verification is classified in to 2 categories namely:
    • Constructional Requirement
    • Performance Requirement

 

    11. All constructional requirements are mandatory and to be design verified by testing.

    12. Many new technical terminologies are being introduced namely - Rated Current of an Assembly, Rated Current of a

          Circuit, Group Rated Current of a circuit, Design Current etc

 

The above shared points are few significant differences between IEC60439 & IEC61439. To get familiarized with the design verification methodologies of IEC61439 and its importance, do visit this forum regularly.

   

Regards

S.Saravanan

Principal Technical Expert

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
Anonymous user
Not applicable

Posted: ‎2020-05-25 09:57 PM

1 Like
0
3054
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-25 09:57 PM

Its now more than 10+ years since the launch of IEC61439 series.The following aspects are addressed more effectively in IEC61439 when compared to its predecessor IEC60439:

 

  1. The number of mechanical operating cycles for main contacts and other parts has been increased to 200.
  2. For thermal evaluation - Verification by calculation is limited to a 630A for single compartments & upto 1600A for multiple compartments.
  3. The rated diversity factor is more clearly described, with each circuit requiring a defined rating.
  4. Neutral cross section is raised to a minimum of 50% of phase cross section, valid for PEN conductors too.
  5. Clearance verification by design may be applied utilizing a ‘safety factor’ of 50%.
  6. Shared responsibility between Original Manufacturer vs. ASSEMBLY Manufacturer.
  7. Agreements between Customer and Manufacturer are more detailed and extended.
  8. Concept of Type Testing & Partially Type Testing are replaced by Design Verification.
  9. Routine Tests are replaced by Routine Verification.
  10. Design verification is classified in to 2 categories namely:
    • Constructional Requirement
    • Performance Requirement

 

    11. All constructional requirements are mandatory and to be design verified by testing.

    12. Many new technical terminologies are being introduced namely - Rated Current of an Assembly, Rated Current of a

          Circuit, Group Rated Current of a circuit, Design Current etc

 

The above shared points are few significant differences between IEC60439 & IEC61439. To get familiarized with the design verification methodologies of IEC61439 and its importance, do visit this forum regularly.

   

Regards

S.Saravanan

Principal Technical Expert

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore