Posted: 2023-12-13 04:24 AM
Ecostruxure Power Commission error code: WCF_server_not_running
"Hi,
I have installed the latest version of the software from https://www.se.com/uk/en/work/products/product-launch/ecostruxure-power-commission/
When I start the program, nothing happens for 5-6 minutes. Then I get the error message from the picture. I can't even get to the login page. Can someone help me?"
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-01-26 12:35 AM
Well, in a way. I dropped using the program. If you're going to install Powertags as I was, you can log onto the Panel Server (PAS600/800) via Network in File Explorer. You can make all the settings through the browser
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-01-31 12:59 AM
Hello
With some computers settings ( IT managment ), the software can meet some issues to start
I advice you to contact your local Customer care center to share the issue and open a case to raise it to our technical team
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-01-25 01:37 AM
Hi, I have the same problem. Did you find a solution for this?
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-01-26 12:35 AM
Well, in a way. I dropped using the program. If you're going to install Powertags as I was, you can log onto the Panel Server (PAS600/800) via Network in File Explorer. You can make all the settings through the browser
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-01-31 12:59 AM
Hello
With some computers settings ( IT managment ), the software can meet some issues to start
I advice you to contact your local Customer care center to share the issue and open a case to raise it to our technical team
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-01-31 10:25 PM
Hello,
One of my client manage to bypass this issue, launching the EPC using right-click and "Run-As-Administrator".
So far I saw this problem only on sistems that use Windows 11.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-02-14 10:58 PM
Thank you for the advice. I tried it also. And now I am able to run EPC-D on my Windows 11 laptop. Thank you!
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-12 06:21 AM
Hi,
this program is still a nightmare! (installed latest version today)
I`am following the procedure with deleting toking:
1. Turn off EPC
2. Go to C:\Users\[username]\AppData\Roaming\Schneider-Electric\Ecoreach
3. Remove userprofile.to and token.to files
4. Start EPC and it will ask you to login (NOTE: You need internet connection for
login or registration procedure).
BR
GIA