Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-03-11 01:50 AM
Hello, I am working on a simple project with a transformer of 2000kVA and 40m cable in the ground. It does not calculate the cables.
Do you have any idea why? Normally it should work. It is not something specially.
Regards and thanks for a quick answer.
Mihaela
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-03-12 02:02 AM . Last Modified: 2025-03-12 02:02 AM
Hello sesa21615_bridg,
Thank you for reaching out to us!
We have reviewed your query and found that you have set the maximum permissible CSA to 240 sqmm for your project.
However, given your project’s cumulative load current and installation method, it exceeds 20 cables/touching circuits, which is not feasible.
In Ecodial, only 20 cables/20 touching circuits including its own cable are allowed for one circuit, so we recommend upgrading the maximum permissible CSA to 300 sqmm.
This adjustment will ensure that Ecodial operates as expected.
I hope this clarifies your query. If you have any further questions, please feel free to ask!
Thanks & Regards,
Team- Ecodial expert support.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-03-11 06:52 AM
Hello @sesa21615_bridg, thank you for your post, we'll come back to you!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-03-12 02:02 AM . Last Modified: 2025-03-12 02:02 AM
Hello sesa21615_bridg,
Thank you for reaching out to us!
We have reviewed your query and found that you have set the maximum permissible CSA to 240 sqmm for your project.
However, given your project’s cumulative load current and installation method, it exceeds 20 cables/touching circuits, which is not feasible.
In Ecodial, only 20 cables/20 touching circuits including its own cable are allowed for one circuit, so we recommend upgrading the maximum permissible CSA to 300 sqmm.
This adjustment will ensure that Ecodial operates as expected.
I hope this clarifies your query. If you have any further questions, please feel free to ask!
Thanks & Regards,
Team- Ecodial expert support.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-03-13 01:02 AM
Hello, Thank you! You are right!
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of