Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Easergy P3U30中的49M保護功能,有沒有所謂的熱積曲線可以設定??

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Easergy P3U30中的49M保護功能,有沒有所謂的熱積曲線可以設定??
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
80
J_Travostino
Sisko J_Travostino Sisko
70
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Power Distribution and Digital Support
Start a Topic
Liujoe
Liujoe
Cadet

Posted: ‎2025-06-12 02:19 AM . Last Modified: ‎2025-06-13 03:22 AM

0 Likes
2
416
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-12 02:19 AM . Last Modified: ‎2025-06-13 03:22 AM

Easergy P3U30中的49M保護功能,有沒有所謂的熱積曲線可以設定??

目前汰換ABB SPAM 150C的保護電驛中有叫得熱積曲線

 

問我們施耐德的P3U30的49M有沒有這個設定,目前我測試的結果都是冷積曲線,不知道如何偵測熱積曲線

Labels
  • Labels:
  • Products
  • Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
Manon_Chaboud
Commander Manon_Chaboud Commander
Commander

Posted: ‎2025-06-13 01:05 AM

0 Likes
0
406
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-13 01:05 AM

Hello @Liujoe, thank you for your post, we'll come back to you!

Reply

Link copied. Please paste this link to share this article on your social media post.

Liujoe
Liujoe
Cadet

Posted: ‎2025-06-16 01:31 AM

0 Likes
0
393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-16 01:31 AM

附圖為實測馬達額定電流情況及設定值

Q1:量測值T%目前恆定在75%左右,若有故障電流產生時T75%~100%(trip)的時間是跑熱機曲線還是冷機曲線有相關值設定???

Q2:量測值T%目前恆定在75%額定電流持續送電時,會不會下降(例:設定熱機曲線變動時)???

 

未命名.jpg

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore