Earth fault loop impedance

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Earth fault loop impedance
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
71
J_Travostino
Sisko J_Travostino Sisko
70
S-W
Commander S-W Commander
66
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Solved
Anonymous user
Not applicable

Posted: ‎2020-12-14 09:29 PM . Last Modified: ‎2022-05-17 02:02 PM

2 Likes
2
5200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-12-14 09:29 PM . Last Modified: ‎2022-05-17 02:02 PM

Earth fault loop impedance

1. Once we got Zs from calculation, So the Zs value referred between distance of cable of Phase & Ground (PE). kindly advise & explain more on how to select the cable size of Phase & Ground (PE), because the cable size is not same.

 

 

2. the Zs value calculated came from Transformer or sources point to earh Fault, What if, There are more level of that points.

how we can calculate the Zs? For example :

200kVA/415/230V, Z= 6% (consists MDB, EMDB, EDB and Final load (Load center))

 

3. HOw can we consider the cable size of Ground (PE) ? If our trip unit of CB has Earth Fault Protection or feeder has Earth Fault Protection Relay

 

So I enclosed the Zs details of CB from SE website

Kindly compare & explain about how different between points & purpose of IEC 60364 & BS 7671 

 

Access the "Moulded Case Circuit Breaker Zs Values" PDF

 

 

Attachments
Labels
  • Labels:
  • Products
  • Tags:
  • Earth fault loop impedance
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
MathieuGuillot
Lieutenant MathieuGuillot Lieutenant
Lieutenant

Posted: ‎2021-01-05 01:35 AM

4 Likes
1
5107
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-01-05 01:35 AM

Hello

 

Thanks for this question at the heart of protection against electric shock in TN system.

 

First comment : there is no major difference between IEC 60364 part 41 and part 54 and BS7671 Chapter 41 and 54. The principle are the same. BS allows to use extraneous conductive part or cable tray as PE where IEC does not but requirement for impedance are the same as for a dedicated conductor.

 

Regarding the Fault loop impedance calculation you may find some helpful material in Electrical Installation guide : https://www.electrical-installation.org/enwiki/TN_system_-_Principle 

 

The fault loop impedance is the sum of source impedance, line impedance and PE impedance. if the cross section of PE is lower than the line it will be considered in PE impedance. The source impedance can be calculated from transformer caracteristics. In your example : 415^2 / 200 000 * 0,06 if Resistive part is neglected.

 

 

The accurate calculation including Resistive and Inductive part of each part of the loop usually requires software tools. Some simplified methods exist (see electrical installation guide).

 

I will ask Neville Watkins to comment on the table we provide for the selection of circuit-breaker according to the Zs.

 

Hope it helps.

 

Happy new year

 

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
MathieuGuillot
Lieutenant MathieuGuillot Lieutenant
Lieutenant

Posted: ‎2021-01-05 01:35 AM

4 Likes
1
5108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-01-05 01:35 AM

Hello

 

Thanks for this question at the heart of protection against electric shock in TN system.

 

First comment : there is no major difference between IEC 60364 part 41 and part 54 and BS7671 Chapter 41 and 54. The principle are the same. BS allows to use extraneous conductive part or cable tray as PE where IEC does not but requirement for impedance are the same as for a dedicated conductor.

 

Regarding the Fault loop impedance calculation you may find some helpful material in Electrical Installation guide : https://www.electrical-installation.org/enwiki/TN_system_-_Principle 

 

The fault loop impedance is the sum of source impedance, line impedance and PE impedance. if the cross section of PE is lower than the line it will be considered in PE impedance. The source impedance can be calculated from transformer caracteristics. In your example : 415^2 / 200 000 * 0,06 if Resistive part is neglected.

 

 

The accurate calculation including Resistive and Inductive part of each part of the loop usually requires software tools. Some simplified methods exist (see electrical installation guide).

 

I will ask Neville Watkins to comment on the table we provide for the selection of circuit-breaker according to the Zs.

 

Hope it helps.

 

Happy new year

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

CAGUPTA
CAGUPTA
Cadet

Posted: ‎2022-10-23 05:57 AM

In response to MathieuGuillot
0 Likes
0
3518
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-23 05:57 AM

Regarding loop impedance, I have a query. How is IEC 60909-0 and IEC TR 60909-4 addressing the issue of 3Zn? When we have a L-G fault current return path, it will flow back in PE conductor accompanying the phase conductors. 

Effectively, the L-G fault current = 3 x U0 / (Z1+Z2+Z0+3ZN). I do not see 3Zn in the calcs as presented by IEC TR 60909-4. In scope sec 1 of the IEC 60909-0, it is written that L-G is beyond the scope of this part of IEC 60909 (page 7). The mention of fourth line and/or earth in the definition of zero sequence short circuit impedance (page 12) is purely for mutual coupling and not for 3Zn calcs. 

Please give your opinion on this.

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of