The Schneider MCCB Max Zs PDF (2010) contains technical information on Moulded Case Circuit Breaker Zs Values (MCCB Zs values) for certain Schneider Electric products. Find out how to calculate max Zs for MCCB for some Schneider Electric products and get information on max Zs values.
Moulded Case Circuit Breaker Zs Values (MCCB Zs Values) Introduction – 1
NSX 100 - 250 Distribution Trip Units – 2
NSX 100 - 250 Motor Protection Trip Units – 3
NSX 100 - 250 Generator Protection Trip Units – 3
NSX 400 - 630 Distribution Trip Units – 4
NSX 400 - 630 Motor Protection Trip Units – 4
NS 630b - 3200 MCCB's – 5
NS 80 Motor Protection MCCB's – 5
NSC 100 Thermal Magnetic MCCB's – 5
“The Zs values are based on disconnection times of either 0.4 or 5 seconds.” – Page 1
“The Zs value for all Circuit Breakers is calculated by dividing the current required to trip the Circuit Breaker at the required tripping time (0.4 or 5 s) into the phase to earth voltage of the system. The current required to trip the circuit breaker can be found by consulting the tripping curve.” – Page 5