ECODIAL CABLE CALCULATION
  • Power Distribution IEC
  • ECODIAL CABLE CALCULATION
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
80
J_Travostino
Sisko J_Travostino Sisko
70
EcoStruxure™ Power Design – Ecodial
acanpolat
Ensign acanpolat Ensign
Ensign
Posted: ‎2021-02-24 04:44 AM . Last Modified: ‎2024-11-22 04:25 AM
6387
I guess it is looking for the Spe> Sph / 2 condition when making ecodial cable calculations. In sections below half of the phase conductor, the protection conductor section gives insufficient warning. Is it true?
  • Power Distribution Software
Genghiz
Captain
Posted: ‎2021-02-24 09:02 PM
Thanks for your query on the 'Ecodial Cable Calculation.'
Automatic Sizing :
There are two verifications done by Ecodial
  1. The automatic sizing of PE conductor is done by respecting the table A.54 of IEC60364-4-54
  1. Then this smallest possible size of PE conductor is also verified, for its thermal withstand against the probable earth fault current (Ief)
Manual Selection :
Once if the PE conductor is manually selected by the user (which is much smaller than the size suggested by table A.54 IEC 60364-5-54) and the verification of the thermal withstand is also not met then – the application is not accepting the selection.
In General :
For more information about the 'sizing of protective earth conductor,' please see the following section of the "Electrical Installation Guide" (link)
Replies 9
Genghiz
Captain
Automatic Sizing :
Manual Selection :
In General :
Posted: ‎2021-03-27 06:02 AM
6255
Ecostructure Ecodial - Residential Reticulation Sample
I would like to see a tutorial on an actual electrical residential installation.
From a normal mini substation / transformer, with kiosks/DB boards, and up to the end user home DB, excluding internal unit design.
Load estimations
diversity factor for amount of houses/loads
cable calculations
voltage drops
kA ratings.
Are there any tutorials of this type out there?
None of the Schneider tutorials cover this completely.
Please assist as I would like to use this software to show the local electrical authority in south africa the calculation figures.
Chris
Genghiz
Captain
Posted: ‎2021-03-31 03:18 AM
In response to Anonymous user
6236
Thanks for your message.
There examples resolved for various scenarios, but they are specific in nature based on the 'load matrix' and the application.
So, we do not have a video - which is specific to a residential complex.
The kind suggestion is ; to kindly comeback to us with the specific load matrix of your example (residential complex); we would be able to assist you in getting the "electrical network solution."
Thanks & Regards,
Team Ecodial
Posted: ‎2021-03-31 10:26 AM
In response to Genghiz
6231
Hello There,
Thanks for the response,
Can we please do an example on the following easy network and loads.
Scenario:
Direct from a 11kV/400v  500kVA mini sub station, on the busbars on the 400V side, a circuit breaker feeding a 12 way kiosk, with an LV cable. The cable is 55m long.
From the 12 way kiosk, there are single feeds to consumer DB boards with 60A single phase loads each.
cable lengths are as follows in meters:
19
34,7
43,7
62,2
62,2
80,3
80,3
74,3
64,6
54,9
45,1
35,5
Thus there are 12 residential units, all fed from a 12 way kiosk, which is in turn fed from the minisub LV side.
Notes:
- The 60A loads are not full loads, but residential circuit breaker sizes, which will have to be diversified load.
- Diversity of 12 residential units is 0.57 in our national standard.
- I am not sure where to put the diversity, on the busbars, or on the loads, or on both.
- the percentage voltage drop from the minisub to the end unit DB, cannot be more than 7.5%
Thank you,
CVM
Genghiz
Captain
Posted: ‎2021-03-31 10:48 PM
6223
Here is our comments;
Scenario 01:
The scenario is specific where all the single phase loads are connected only to L1-N.
Step 1 :
All the loads (60A) are connected to the same line (L1 - N); will leads to the total demand as 499 kVA.
The diversity is 1.0 by default at the application. So, The proposed transformer rating is 500 kVA.
Step 2 :
The diversity (0.57 as per your country standard) must be applied to the Main Switchboard level.
This has optimized the "actual demand" as 284 kVA. So,
The proposed transformer rating is 300 kVA. (after applied the diversity)
Genghiz
Captain
Posted: ‎2021-03-31 11:13 PM
6221
Scenario 2 :
This scenario is so specific, that all the single phase loads are "distributed evenly among all the 3 phases" between (L1-N and L2-N and L3-N); Defined by the 'Connection as Automatic' as shown in the image.
Step 1:
All the loads (60A) are  distributed evenly between the 3 phases.
This leads to the total demand as 166 kVA.
So, The proposed transformer rating is 250 kVA.
Step 2:
The diversity is 0.57 is applied at the switchboard level.
This leads to the actual demand as 94.8 kVA
So, The proposed transformer rating is 100 kVA
Genghiz
Captain
Posted: ‎2021-03-31 11:17 PM
Conclusion :
  • The Diversity Factor is helping you to optimize the source sizing.
  • However the connection (Either loading only a single line Or Distributing between all the 3 lines) is also important to get the optimized source sizing.
Posted: ‎2021-04-01 03:07 AM
6210
Thank you,
I will then in future use the diversity on the main busbar of the kiosk. If there are more kiosks, do I put the diversity on each of the busbars downstream?
Also I see I do not need to put in an extra busbar between the minisub and the 12way kiosk as I did.
I am interested in the kA ratings three phase and single phase to size the circuit breakers.
Genghiz
Captain
Posted: ‎2021-04-01 06:14 AM
The "Diversity Factor" should be applied at the "Switchboard" (where we have more than one load/feeders are connected).
  • In my example; I have only one switchboard (which was a main switchboard), So I have applied the diversity factor at that switchboard.
  • As per your "single line diagram," you should apply the diversity at 'switch board' where all the load circuits (22, 23, 24...) are connected.
Thank you