Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

DC application

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • DC application
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
78
J_Travostino
Sisko J_Travostino Sisko
70
S-W
Commander S-W Commander
67
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2022-07-16 11:46 PM . Last Modified: ‎2022-07-18 03:31 AM

0 Likes
6
2397
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-16 11:46 PM . Last Modified: ‎2022-07-18 03:31 AM

DC application

i want to use nsx100f 4x100A 4p4d circuit breaker in a DC Application, my system voltage is 48v, 100A DC will pass through each pole of the breaker, i will use two of them one for positive and the other for negative pole. Do this circuit breaker works properly in such situation 

Labels
  • Labels:
  • Products
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
RHH
Commander | EcoXpert Master RHH Commander | EcoXpert Master
Commander | EcoXpert Master

Posted: ‎2022-07-18 04:18 AM . Last Modified: ‎2022-07-18 04:25 AM

0 Likes
5
2367
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-18 04:18 AM . Last Modified: ‎2022-07-18 04:25 AM

Dear @Anonymous user ,

I suggest you use the specific DC NSX found here; NSX for DC 
And use a TM100 DC trip unit with it.

Therefor I cannot tell you the DC specifics of a non DC NSX, as its probably not tested for it.

 

The standard NSX100F states; 

network type

AC



Hope this helps you out.


 


Kind regards,

Rick

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
RHH
Commander | EcoXpert Master RHH Commander | EcoXpert Master
Commander | EcoXpert Master

Posted: ‎2022-07-18 04:18 AM . Last Modified: ‎2022-07-18 04:25 AM

0 Likes
5
2368
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-18 04:18 AM . Last Modified: ‎2022-07-18 04:25 AM

Dear @Anonymous user ,

I suggest you use the specific DC NSX found here; NSX for DC 
And use a TM100 DC trip unit with it.

Therefor I cannot tell you the DC specifics of a non DC NSX, as its probably not tested for it.

 

The standard NSX100F states; 

network type

AC



Hope this helps you out.


 


Kind regards,

Rick
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2022-07-18 11:19 AM

In response to RHH
0 Likes
4
2347
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-18 11:19 AM

Dear @RHH ,

 

thanks for ur reply, but what makes me confused that i found the following in FAQ schnieder and that was the reply 

(CAN NSX AC BREAKER be USED IN DC APPLICATIONS ?

ONLY the following 2 categories of the compact NSX AC MCCB are proven to operate under DC rated operatinal voltage as shown in the attached catalogue Panorama.
1- The compact NSX AC MCCB 1 Pole - from 100 to 250A only - can be used under 250VDC rated operational voltage .
2- The compact NSX AC MCCB 2 Poles - from 100 to 250A only - can be used under 500VDC rated operational voltage.
Kindly use the below link to download the Schneider offer for DC networks Circuit breakers from 16 to 4000A Compact NSX DC & Masterpact NW DC.
https://www.se.com/uk/en/download/document/LVPED)

thats why iam asking if i can use NSX AC type on my application since in our country the NSX DC is not available 

regards 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Berkhof
Lieutenant | EcoXpert Master Berkhof Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2022-07-18 11:27 PM

In response to Anonymous user
0 Likes
3
2331
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-18 11:27 PM

Hi Ayman,

 

I think the FAQ refers to the 1P and 2P NSX. This one is for both AC and DC.

 

The frame is really meant for AC. There is a Micrologic that can be used in both an AC and a DC NSX, The TM-G. 

But I don't recommend using AC components for DC.

 

Kind regards,

 

John

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Christian_Bach
Lt. Commander Christian_Bach Lt. Commander
Lt. Commander

Posted: ‎2022-07-19 12:03 AM

In response to Berkhof
2 Likes
2
2323
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-19 12:03 AM

Hi @Anonymous user ,

 

First, very important point, never use a circuit breaker for performances that are not claimed on the catalog, you would not be covered by the manufacturer and authorities in case of issue, on top of potential safety risks of course.

 

Second, @Berkhof , a Micrologic shall NOT be used in DC, the current sensors DO NOT work at all !

 

I think for your application a 2P NSX might be ok.

 

Christian

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Berkhof
Lieutenant | EcoXpert Master Berkhof Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2022-07-19 01:00 AM

In response to Christian_Bach
1 Like
1
2315
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-19 01:00 AM

Hi @Christian_Bach,

 

According to the Schneider documentation, the TM-G is suitable for both AC and DC.

 

https://www.se.com/ww/en/product/C164MG125/trip-unit-tm125g-compact-nsx160-4-poles-4d-neutral-fully-...

 

TM-G.PNG

 

Maybe I shouldn't have called it a Micrologic but a Trip unit 😉

 

 

Kind regards,

 

John

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Christian_Bach
Lt. Commander Christian_Bach Lt. Commander
Lt. Commander

Posted: ‎2022-07-19 01:08 AM

In response to Berkhof
2 Likes
0
2313
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-19 01:08 AM

Hi @Berkhof ,

 

Thanks for your inputs. TMD or TMG are thermal magnetic trip units. TMG have double AC DC markings, you are right, but it must be used with a DC breaking block in this case.

 

And sorry if my previous statement was a bit "rude", it was just to make crystal clear that Micrologic are not working is DC and thus avoid misuse 😉.

 

This is Schneider vocabulary, Micrologic wording applies to electronic protection only.

 

Thanks,

Christian 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore