63A 8P Switch Disconnector

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • 63A 8P Switch Disconnector
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
80
J_Travostino
Sisko J_Travostino Sisko
70
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Expert on Demand for Standards & Regulations

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Start a Topic
Solved
Peter_Hall
Lt. Commander | EcoXpert Master Peter_Hall Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master

Posted: ‎2022-07-14 02:28 AM

1 Like
9
4030
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-14 02:28 AM

63A 8P Switch Disconnector

Can anyone please give me the part number for an 8P 63A disconnector? I'm looking at using one for a bypass on a change over panel.

Labels
  • Labels:
  • Power Availability
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Christian_Bach
Lt. Commander Christian_Bach Lt. Commander
Lt. Commander

Posted: ‎2022-07-18 05:41 AM

In response to RHH
2 Likes
1
3938
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-18 05:41 AM

Hi @RHH ,

 

The request seems to be a 8P switch, not a manual transfer switch (I-O-II). I am interested to understand the application need, let's wait for the information.

 

Christian

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
RHH
Commander | EcoXpert Master RHH Commander | EcoXpert Master
Commander | EcoXpert Master

Posted: ‎2022-07-14 02:45 AM . Last Modified: ‎2022-07-14 02:46 AM

1 Like
7
4025
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-14 02:45 AM . Last Modified: ‎2022-07-14 02:46 AM

Hello @Peter_Hall ,

 

I attached the Schneider Electric Transferpact catalogue in PDF.
You can use accessoiries like; mechanical interlocking - for devices with extended rotary handle - 40...160 A 

All is described in the PDF attached.

Hope this is of any help!



 


Kind regards,

Rick
Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Peter_Hall
Lt. Commander | EcoXpert Master Peter_Hall Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master

Posted: ‎2022-07-14 02:59 AM

In response to RHH
0 Likes
6
4021
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-14 02:59 AM

Hi @RHH,

 

Thank you for your reply. That one will do for one switch. however, it was the wrap around switch for the mains supply that i was looking for. This needs to be an 8 pole gang operated switch 2 position.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Christian_Bach
Lt. Commander Christian_Bach Lt. Commander
Lt. Commander

Posted: ‎2022-07-18 12:12 AM

In response to Peter_Hall
1 Like
5
3960
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-18 12:12 AM

Hi @Peter_Hall ,

 

Sorry, probably my english but I don't understand your need. Could you please post a schematic ?

 

Thanks,

Christian

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Peter_Hall
Lt. Commander | EcoXpert Master Peter_Hall Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master

Posted: ‎2022-07-18 12:57 AM

In response to Christian_Bach
0 Likes
4
3956
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-18 12:57 AM

Hi @Christian_Bach,

 

No problems. It is though very simple. the unit needs to be as:

 

8 poles.

2 position (off/on).

Single central operating handle.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Christian_Bach
Lt. Commander Christian_Bach Lt. Commander
Lt. Commander

Posted: ‎2022-07-18 05:30 AM

In response to Peter_Hall
0 Likes
0
3941
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-18 05:30 AM

Hi @Peter_Hall ,

 

Thanks, so basic switch with 8P operated by a single actuator.

 

I am investigating with my colleagues from final distribution products, would a toggle type actuator fit your need ?

 

Would it be possible to share your Bypass schematics (even in private message) ?

 

Thanks,

Christian

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

RHH
Commander | EcoXpert Master RHH Commander | EcoXpert Master
Commander | EcoXpert Master

Posted: ‎2022-07-18 05:38 AM . Last Modified: ‎2022-07-18 05:49 AM

In response to Peter_Hall
0 Likes
2
3940
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-18 05:38 AM . Last Modified: ‎2022-07-18 05:49 AM

I think I know what you mean, the most common (8P) is 1-0-2 though.

 

Like the jpg files I attached to this post. Coming from our workshop.



Kind regards,

Rick
Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Christian_Bach
Lt. Commander Christian_Bach Lt. Commander
Lt. Commander

Posted: ‎2022-07-18 05:41 AM

In response to RHH
2 Likes
1
3939
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-18 05:41 AM

Hi @RHH ,

 

The request seems to be a 8P switch, not a manual transfer switch (I-O-II). I am interested to understand the application need, let's wait for the information.

 

Christian

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

RHH
Commander | EcoXpert Master RHH Commander | EcoXpert Master
Commander | EcoXpert Master

Posted: ‎2022-07-18 05:46 AM

In response to Christian_Bach
1 Like
0
3933
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-18 05:46 AM

@Christian_Bach ,

 

Yes, indeed.
Curious we are 🙂




Kind regards,

Rick
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Berkhof
Lieutenant | EcoXpert Master Berkhof Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2022-07-18 06:25 AM

1 Like
0
3921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-18 06:25 AM

Hi @Peter_Hall ,

 

Maybe 2x NSXna with a MN coil will do the trick? ( 2x C114100LS 2x LV426806 )

 

Connect the Q1 MN coil to Q2 and the Q2 MN coil to Q1.

 

As soon u switch one of the to breakers open than the other one will disconnect aswell.

 

Closing the 2 breakers will be a 2 handed operation. or with a bypass on the MN coils.

 

Kind regards,

 

John

 

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore