ComPacT NSX Maintenance recomandation

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • ComPacT NSX Maintenance recomandation
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
80
J_Travostino
Sisko J_Travostino Sisko
70
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Expert on Demand for Standards & Regulations

Related Products
product field
Schneider Electric
ComPact NSX
product field
Schneider Electric
ComPacT NSX, new generation
product field
Schneider Electric
ComPacT NSXm, new generation
field url
Schneider Electric
ComPacT for DC networks, new generation
Load more

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Start a Topic
Solved
Gregoire_Brun
Commander Gregoire_Brun Commander
Commander

Posted: ‎2022-04-04 08:31 AM . Last Modified: ‎2022-04-05 12:52 AM

1 Like
5
4378
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-04-04 08:31 AM . Last Modified: ‎2022-04-05 12:52 AM

ComPacT NSX Maintenance recomandation

Hello All

From your knowledge and experience, what are the maintenance recommandation you give to your customers about MCCB's when you design an equipment?

 

Your feedback is very important and helpful for us.

 

Thanks a lot.

 

Gregoire Brun
Breaker Product Expert
Labels
  • Labels:
  • Operations & Services
  • Products
  • Safety - People Safety
  • Schneider Partner Programs
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2022-04-19 12:53 AM . Last Modified: ‎2022-04-21 09:13 PM

1 Like
2
4182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-04-19 12:53 AM . Last Modified: ‎2022-04-21 09:13 PM

Hi Gregoire,

 

According to my experiences, there are some maintenance that can be propose to users :

 

A. For high current Circuit Breakers (LV / MV) :

  1. Preventive maintenance such as :
    1. Visual check (Contact wear, sign of Burned, leak, water, etc)
    2. Cleaning & re-greasing on the operating mechanism (moving parts)
    3. Some parts may need Electrical Grease (Finger Contact)
    4. Torqing on the bolt & nuts to avoid loosen connections that create heat. Consult manufacurer for torq value.
  2. Predictive Maintenance using Diagnostic tools
    1. Circuit breaker diagnostic tools to check any deteriorating performance parts (Opening & closing speed, over travel, maoin contact wear, etc)
    2. Check on the contact resistance
    3. Check on the tripping curve of the Tripping Unit.

 

B. For low current circuit breakers such as MCCB

  1. Preventive maintenance such as :
    1. Visual check (sign of Burned, leak, water, etc)
    2. Cleaning & re-greasing on the operating mechanism (moving parts)
    3. Torqing on the bolt & nuts to avoid loosen connections that create heat. Consult manufacurer for torq value.
  2. Predictive maintenance
    1. Using Thermography. With the thermal imaging camera or just spot measurement you can detect any potential problem such as loosen contact (higher heat on connections) or overload (heat on the MCCB).
    2. Some MCCB have internal embeded facility to check for the internal contact wear (Self diagnostic)
    3. Check on the tripping curve using Micrologic testing tools

 

The are many level of maintenance that can be done by user, trained engineer or by Manufacturer.

The Periodic maintenance Schedule is also can be defined based on criticality of the load.

 

Hope help.

 

Preventive maintenance.jpg

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Peter_Hall
Lt. Commander | EcoXpert Master Peter_Hall Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master

Posted: ‎2022-04-19 01:06 AM

In response to HelvinHermanT
1 Like
1
4178
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-04-19 01:06 AM

Some interesting thoughts on this topic.

 

I never cease to be amazed that a customer buys a brand new LV switchboard and then hands over the maintenance to a contractor who cannot provide any evidence of manufacturers training or authorisation. When the works are completed the customer is left with very little or no evidence that the work has been carried out. Who would buy a brand new BMW and hand it over to a friend who is 'good' with cars to look after and expect BMW to pick up any warranty claims found by this 'friend'?

 

With the advent of the new range of communicating devices servicing of devices and service history should be much easier. Servicing could be monitored via the adoption of 'Service Centre' badges. EPC could be adapted to run a servicing regime on devices. This would leave a service history stamp on the device and upload service information to FE Logbook for the customer to access. All service steps could be incorporated into EPC., This would ensure a level is maintained and cannot be open to interpretation or confusion as to just what is required on a certain device. 

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Gregoire_Brun
Commander Gregoire_Brun Commander
Commander

Posted: ‎2022-05-13 06:17 AM . Last Modified: ‎2022-05-13 08:42 AM

In response to Anonymous user
0 Likes
0
3888
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-13 06:17 AM . Last Modified: ‎2022-05-13 08:42 AM

We do like explain by @HelvinHermanT 

And it's specified in all user guide we edit for all products.

Document can be find in our website ( tell me if you need one in particular)

 

 

Gregoire Brun
Breaker Product Expert

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Gregoire_Brun
Commander Gregoire_Brun Commander
Commander

Posted: ‎2022-05-13 06:20 AM . Last Modified: ‎2022-05-13 08:44 AM

In response to Peter_Hall
0 Likes
0
3887
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-13 06:20 AM . Last Modified: ‎2022-05-13 08:44 AM

Hi Peter 

Your example of the car is good because even if you buy a Dacia or a Porsche, every year you go to the garage to change oils and make some maintenance checks. That's what we fiel for electrical device as something needed...

 

Gregoire Brun
Breaker Product Expert

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2022-04-10 10:58 PM

1 Like
1
4285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-04-10 10:58 PM

Hello @Gregoire_Brun ,

 

Aren't there any recommendations made by manufacturers as Schneider Electric or others?

What about the warranty if customers don't follow them?

 

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2022-04-19 12:53 AM . Last Modified: ‎2022-04-21 09:13 PM

1 Like
2
4183
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-04-19 12:53 AM . Last Modified: ‎2022-04-21 09:13 PM

Hi Gregoire,

 

According to my experiences, there are some maintenance that can be propose to users :

 

A. For high current Circuit Breakers (LV / MV) :

  1. Preventive maintenance such as :
    1. Visual check (Contact wear, sign of Burned, leak, water, etc)
    2. Cleaning & re-greasing on the operating mechanism (moving parts)
    3. Some parts may need Electrical Grease (Finger Contact)
    4. Torqing on the bolt & nuts to avoid loosen connections that create heat. Consult manufacurer for torq value.
  2. Predictive Maintenance using Diagnostic tools
    1. Circuit breaker diagnostic tools to check any deteriorating performance parts (Opening & closing speed, over travel, maoin contact wear, etc)
    2. Check on the contact resistance
    3. Check on the tripping curve of the Tripping Unit.

 

B. For low current circuit breakers such as MCCB

  1. Preventive maintenance such as :
    1. Visual check (sign of Burned, leak, water, etc)
    2. Cleaning & re-greasing on the operating mechanism (moving parts)
    3. Torqing on the bolt & nuts to avoid loosen connections that create heat. Consult manufacurer for torq value.
  2. Predictive maintenance
    1. Using Thermography. With the thermal imaging camera or just spot measurement you can detect any potential problem such as loosen contact (higher heat on connections) or overload (heat on the MCCB).
    2. Some MCCB have internal embeded facility to check for the internal contact wear (Self diagnostic)
    3. Check on the tripping curve using Micrologic testing tools

 

The are many level of maintenance that can be done by user, trained engineer or by Manufacturer.

The Periodic maintenance Schedule is also can be defined based on criticality of the load.

 

Hope help.

 

Preventive maintenance.jpg

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Peter_Hall
Lt. Commander | EcoXpert Master Peter_Hall Lt. Commander | EcoXpert Master
Lt. Commander | EcoXpert Master

Posted: ‎2022-04-19 01:06 AM

In response to HelvinHermanT
1 Like
1
4179
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-04-19 01:06 AM

Some interesting thoughts on this topic.

 

I never cease to be amazed that a customer buys a brand new LV switchboard and then hands over the maintenance to a contractor who cannot provide any evidence of manufacturers training or authorisation. When the works are completed the customer is left with very little or no evidence that the work has been carried out. Who would buy a brand new BMW and hand it over to a friend who is 'good' with cars to look after and expect BMW to pick up any warranty claims found by this 'friend'?

 

With the advent of the new range of communicating devices servicing of devices and service history should be much easier. Servicing could be monitored via the adoption of 'Service Centre' badges. EPC could be adapted to run a servicing regime on devices. This would leave a service history stamp on the device and upload service information to FE Logbook for the customer to access. All service steps could be incorporated into EPC., This would ensure a level is maintained and cannot be open to interpretation or confusion as to just what is required on a certain device. 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Gregoire_Brun
Commander Gregoire_Brun Commander
Commander

Posted: ‎2022-05-13 06:17 AM . Last Modified: ‎2022-05-13 08:42 AM

In response to Anonymous user
0 Likes
0
3889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-13 06:17 AM . Last Modified: ‎2022-05-13 08:42 AM

We do like explain by @HelvinHermanT 

And it's specified in all user guide we edit for all products.

Document can be find in our website ( tell me if you need one in particular)

 

 

Gregoire Brun
Breaker Product Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Gregoire_Brun
Commander Gregoire_Brun Commander
Commander

Posted: ‎2022-05-13 06:20 AM . Last Modified: ‎2022-05-13 08:44 AM

In response to Peter_Hall
0 Likes
0
3888
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-13 06:20 AM . Last Modified: ‎2022-05-13 08:44 AM

Hi Peter 

Your example of the car is good because even if you buy a Dacia or a Porsche, every year you go to the garage to change oils and make some maintenance checks. That's what we fiel for electrical device as something needed...

 

Gregoire Brun
Breaker Product Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore