Can you help me to select the right metering devices?

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • Can you help me to select the right metering devices?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
80
J_Travostino
Sisko J_Travostino Sisko
70
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Expert on Demand for Standards & Regulations

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-01-11 06:14 AM . Last Modified: ‎2022-02-02 01:51 AM

0 Likes
6
3949
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-01-11 06:14 AM . Last Modified: ‎2022-02-02 01:51 AM

Can you help me to select the right metering devices?

Do you have a presentation of the different metering solutions that we can implement in a Smart Panel ?

Mainly to select the right ones.

 

Thanks

Labels
  • Labels:
  • Connectivity
  • Energy management
  • Products
  • Sustainability
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Fabien_Mastrot
Fabien_Mastrot Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2021-01-12 12:54 AM

2 Likes
2
3935
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-01-12 12:54 AM

Hello,

To select the right metering solutions in a Smart Panel , it might be a difficult process. To simplify your life , we propose to use a simple Equation to apply .

According to the Facility needs and the type of architecture, we recommand to you the most relevant choice. 

Discover in our ppt done by our Expert Thomas Peregrin,  the principle of the selection with an example of architecture.

What do you think about that ? don t hesitate to comment ?

Thanks

Fabien

Fabien Mastrot
EcoXpert global badge owner

See Answer In Context

Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2022-05-17 04:26 AM

1 Like
2
2994
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-17 04:26 AM

HI, 

 

You can find some options in the MEASURE part of Smart Panel Presentation (Page 15).

 

Micrologic Trip Units, PowerTag wireless energy sensor, Acti 9 energy meters & PowerLogic meters.

 

Measure 2.jpgMeasure 1.jpg

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Fabien_Mastrot
Fabien_Mastrot Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2021-01-12 12:54 AM

2 Likes
2
3936
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-01-12 12:54 AM

Hello,

To select the right metering solutions in a Smart Panel , it might be a difficult process. To simplify your life , we propose to use a simple Equation to apply .

According to the Facility needs and the type of architecture, we recommand to you the most relevant choice. 

Discover in our ppt done by our Expert Thomas Peregrin,  the principle of the selection with an example of architecture.

What do you think about that ? don t hesitate to comment ?

Thanks

Fabien

Fabien Mastrot
EcoXpert global badge owner
Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-01-27 12:20 AM

In response to Fabien_Mastrot
0 Likes
1
3875
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-01-27 12:20 AM

Hello,

in your ranges I have seen something as Powertag for the Compact NSXm ?  a bit strange ?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Gregoire_Brun
Commander Gregoire_Brun Commander
Commander

Posted: ‎2022-05-13 06:31 AM

In response to Anonymous user
0 Likes
0
3089
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-13 06:31 AM

Very intersting question, it depends about what you want to do with the measuring.

  • Did you want a measuring on local or you can read by remote?
  • Did you want a very smal precision class of measuring or not ?
  • Did you want to use the measure to identify area with high leavel of consumssion ?
  • Did you want to use it to make some electrical diagnostic in case of incident?
  • Did you have volume constraint on your equipment ?
  • etc...

Don't hesitate if you have some other questions I don't list to help you to make the right choice between our diferents offer.

Gregoire Brun
Breaker Product Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2022-05-17 04:26 AM

1 Like
2
2995
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-17 04:26 AM

HI, 

 

You can find some options in the MEASURE part of Smart Panel Presentation (Page 15).

 

Micrologic Trip Units, PowerTag wireless energy sensor, Acti 9 energy meters & PowerLogic meters.

 

Measure 2.jpgMeasure 1.jpg

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

J_Travostino
Sisko J_Travostino Sisko
Sisko

Posted: ‎2022-05-17 08:45 AM

In response to HelvinHermanT
0 Likes
0
2985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-17 08:45 AM

 
Julien Travostino
Power Distribution & Digital forum community owner
Power Products Div.
Reply

Link copied. Please paste this link to share this article on your social media post.

J_Travostino
Sisko J_Travostino Sisko
Sisko

Posted: ‎2022-05-17 08:45 AM

In response to HelvinHermanT
1 Like
0
2985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-17 08:45 AM

Thanks @HelvinHermanT for sharing this.

 

Can you please give us the link toward the full document? 

Thanks.

 

 

Julien Travostino
Power Distribution & Digital forum community owner
Power Products Div.
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore