Blokset switchboard horizontal transport
Hello all,
I got an issue on a Blokset switchboard delivery.
I would need to carry it horizontally.
Could you validate please I can ship it this way?
Best regards
Esperanto
- Labels:
-
Products
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions

Posted: 2019-09-06 03:39 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-09-06 03:39 AM
Dear Esperanto,
Good afternoon.
We do not recommend transporting Blokset panel in Horizontal position.
The panels are intended to be used in vertical position. During the designing of the panel, care has been taken to ensure to withstand the forces which is generated because of vibration in vertical position only.
During transportation in horizontal position, the Devices, busbars and sheet metal parts may get damage because of the vibrations generated during the transportation. This will affect the performance of the switchboard.
So, we do not recommend transporting in Horizontal position. It should be always in Vertical position only.
I hope it is clear now.
Best Regards
Vij
Link copied. Please paste this link to share this article on your social media post.

Posted: 2019-09-06 03:39 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-09-06 03:39 AM
Dear Esperanto,
Good afternoon.
We do not recommend transporting Blokset panel in Horizontal position.
The panels are intended to be used in vertical position. During the designing of the panel, care has been taken to ensure to withstand the forces which is generated because of vibration in vertical position only.
During transportation in horizontal position, the Devices, busbars and sheet metal parts may get damage because of the vibrations generated during the transportation. This will affect the performance of the switchboard.
So, we do not recommend transporting in Horizontal position. It should be always in Vertical position only.
I hope it is clear now.
Best Regards
Vij
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-05-17 04:21 AM
When it comes to material handling like lifting, loading, unloading and installation, Blokset provides 2 options which ensures use of vertical position
1) It can be carried from forklift
2) It can be lifted by using lifting rings provided on each column or shipping sections
Product manager - Blokset, LV switchboard