Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

BIM Electrical Design Plugin

Power Distribution and Digital Support

Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Power Distribution and Digital Support
  • BIM Electrical Design Plugin
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Genghiz
Captain Genghiz Captain
93
Gregoire_Brun
Commander Gregoire_Brun Commander
80
J_Travostino
Sisko J_Travostino Sisko
70
View All

Recommended Forums

  • Comunidade de Soluções Elétricas

  • Expert on Demand for Standards & Regulations

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Power Distribution and Digital Support
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2020-11-05 11:52 PM . Last Modified: ‎2020-11-20 08:10 AM

1 Like
10
5773
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-05 11:52 PM . Last Modified: ‎2020-11-20 08:10 AM

BIM Electrical Design Plugin

Hi to all!

Did not find the necessary forum therefore I write here. Who can I ask questions / comments about the BIM Electrical Design plugin for Revit?

Thanks!

Labels
  • Labels:
  • Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2020-11-09 10:18 PM

In response to Jean_Commeignes
1 Like
0
5677
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-09 10:18 PM

Hi, Jean!

 

I found the necessary information.

Plugin page (RU, ENG)

 

Support:  bim@se.com 

Sent a letter with a list of questions. Promptly responded.

 

There is also a branch on the Autodesk forum (RU):

forums.autodesk.com 

 

Thanks for the help!

 

See Answer In Context

  • Tags:
  • bimed
  • bimelectricaldesign
  • english
  • Здравствуйте! я не могу войти в учетную запись BIM ElectricalDesign. ввожу имя и пароль
  • потом система зависает с белым окошком на экране. установлен Revit 2019 и 2024
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
Jean_Commeignes
Administrator Jean_Commeignes Administrator
Administrator

Posted: ‎2020-11-06 05:57 AM

1 Like
7
5764
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-06 05:57 AM

@Genghiz @sesa25143_bridg

Could you please answer avs-electric on that, as i can understand that it is Ecodial related?

 

Best

 

Jean COMMEIGNES
Schneider Electric Community Manager for Power & Building
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Genghiz
Captain Genghiz Captain
Captain

Posted: ‎2020-11-08 10:50 PM

In response to Jean_Commeignes
0 Likes
0
5745
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-08 10:50 PM

Hello Jean

The BIM Electrical Design Plugin for Revit - Is not related to the Ecodial application. 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

J_Travostino
Sisko J_Travostino Sisko
Sisko

Posted: ‎2020-11-08 11:56 PM

2 Likes
1
5740
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-08 11:56 PM

Hi @Anonymous user 

 

In order to be able to provide you an accurate support, can you please precise your country location?

 

On which Revit plug-in you may have questions/comments (BIM models, LayoutFast,...)?

 

Thks for information

 

 

Julien Travostino
Power Distribution & Digital forum community owner
Power Products Div.
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-11-09 12:08 AM

In response to J_Travostino
0 Likes
0
5731
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-09 12:08 AM

Hi, Julien.

 

I'm from Ukraine, Kyiv.

I have questions about the "BIM Electrical Design Plugin" plugin for Revit. Our company is implementing a pilot project to power the office center in a Revit environment using this plugin. After a week of work, our team found a number of bugs (or maybe it's features =)), I want to discuss with experts.

 

Thanks!

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-11-09 04:49 AM

In response to Jean_Commeignes
0 Likes
5
5710
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-09 04:49 AM

Revit est logiciel qui appartient à AUTODESK, son utilisation nécessite une licence de leurs part.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-11-09 05:14 AM

In response to Anonymous user
0 Likes
4
5705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-09 05:14 AM

Yes, of course, I have licensed software.

My question is not about Revit (Autodesk), but about the BIM Electrical Design Plugin (from Schneider Electric).

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-11-09 05:56 AM . Last Modified: ‎2020-11-09 08:23 AM

In response to Anonymous user
1 Like
3
5701
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-09 05:56 AM . Last Modified: ‎2020-11-09 08:23 AM

Téléchargez la version fournie d'un plug-in et consultez les informations détaillées et la documentation possible à partir du portail partenaire Schneider Electric pour les concepteurs. La mise à jour directement à partir d'un plug-in BIM Electrical Design est disponible pour les utilisateurs de la version 2.0.

 

Si vous n'avez pas réussi télécharger la mise à jour et à résoudre le problème de bugs, il est conseillé de contacter votre fournisseur de licence chez vous.

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-11-09 06:13 AM

In response to Anonymous user
0 Likes
2
5696
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-09 06:13 AM

To be exact - the current version 2.1.31.

Thanks for the help, I'll contact Autodesk

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Jean_Commeignes
Administrator Jean_Commeignes Administrator
Administrator

Posted: ‎2020-11-09 11:35 AM

In response to Anonymous user
1 Like
1
5684
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-09 11:35 AM

Hello avs, 

 

I wish make you aware that I could identify people in charge of this Revit Plug-in.

I believe they are experts you wish get in touch with.

 

I wish they get back to you asap.

 

Best

Jean COMMEIGNES
Schneider Electric Community Manager for Power & Building
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-11-09 10:18 PM

In response to Jean_Commeignes
1 Like
0
5678
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-09 10:18 PM

Hi, Jean!

 

I found the necessary information.

Plugin page (RU, ENG)

 

Support:  bim@se.com 

Sent a letter with a list of questions. Promptly responded.

 

There is also a branch on the Autodesk forum (RU):

forums.autodesk.com 

 

Thanks for the help!

 

  • Tags:
  • bimed
  • bimelectricaldesign
  • english
  • Здравствуйте! я не могу войти в учетную запись BIM ElectricalDesign. ввожу имя и пароль
  • потом система зависает с белым окошком на экране. установлен Revit 2019 и 2024
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore