Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Join experts & peers to learn, share and engage about the key trends of electrical distribution around safety, availability, efficiency and connectivity, as well as power standards & regulations. From design to implementation and operation, let’s discuss how digital and software are transforming your business and your day-to-day work.
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-18 10:23 AM
We are including NSX circuit breakers with Micrologic 2.2 trip units for some of the final circuits in our main distribution cabinet ( C16N4 with C1642D160)
When verifying Zs × Ia ≤ Uo condition according IEC 60364 4 41 can we use Isd setting that can be adjusted from 1.5 - 10xIr and what is max break time in that case. I see that there is no adjustable time delay and maximum break time is 80ms which is well under allowed 0.4s but is that total break time.
I ask this because Ii is too high for some applications so it would be more convenient to use Isd setting.
Is there any Schneider documentation that explains these settings and their use.
Thank You
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.