2024-09-25 05:08 AM - diedit 2024-09-26 12:51 AM
I need to connect 7 3-wire PNP sensors to a PLC.
To save on wiring, is it possible to use common supply and ground for them from the PLC and 1 signal per sensor? So this would become 9 cores in total in a single multicore cable?
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
pada 2024-10-17 05:07 AM
I see no problem on a solution like that if all signals got to the same DI card or on the same oboard DI.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
pada 2024-10-17 05:07 AM
I see no problem on a solution like that if all signals got to the same DI card or on the same oboard DI.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
pada 2024-10-17 02:11 PM
Thank you