PLC Club Indonesia
Wadah diskusi seputar PLC,HMI, SCADA dan semua hal seputar otomasi pada proses industri, baik mengenai hal teknis, informasi terbaru dan juga seputar bisnis. Forum ini terbuka unutuk semua system integrator industrial di Indonesia
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-01-25 01:58 AM
Dear All
Apakah kita bisa melakukan hot swap (kita bisa mengganti modul yang rusak tanpa mematikan power dari rack PLC) pada semua modul M580 (baik itu CPU, IO, power supply dan modul komunikasi) termasuk juga modul untuk safety PLC dan redundant CPU?
Terima kasih
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-01-29 11:34 PM . Last Modified: 2024-01-29 11:36 PM
Hello Adrians,
You can find this info in many places but it is mentioned clearly on the website in the description part as the print screen
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-01-25 10:02 PM
Hello Adrian,
after getting support from Google Translate :), all X80 Modules have hot Swapp features and can easily be replaced or removed without any problem in the remaining system components, regarding the CPUs you can replace the standby CPU or communication module in case the Main CPU and CP are working properly.
The power supply shall be redundant to replace one of the bundles.
For more info please check
https://iportal2.schneider-electric.com/Contents/docs/SQD-490NAC0100_USER%20GUIDE.PDF
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-01-25 11:34 PM
Hello Mnabil
Thank you for the answer,
I have tried to find/search the Hot standby planning system pdf but I can't find the page which show any statement that we can just plug out any broken module (CPU, communication, or IO module) and then plug in the replacement module without turning off the power of the back plane (hot swapping the module).
but incase I miss the information, can you show me in which page can we find the Hot Swap statement?
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-01-29 12:08 AM
Hello Mnabil
Thank you for the answer,
I have tried to find/search the attached pdf, but I can't find any page that state we can plug off any broken module (CPU, communication, or IO module) and just plug in the replacement module without turn off the power of the PLC rack.
But incase I miss the information, can you show me in which page of the pdf does the hot swap statement be explained?
Thank you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.