Bagaimana cara mengukur current analog input yang masuk ke M221?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-11-08 04:44 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-11-08 04:38 AM
bisa diukur dengan cara di seri dengan sensornya yang terpasanng.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-11-08 04:44 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-11-08 04:44 AM
apabila sensornya sudah terpasang pada module analognya, bisa juga dengan cara melihat pada nilai integer dari memory address channel analognya ( dengan catatan sensor analognya sudah di scaling dengan benar ) sehingga tampilan nilai integer pada alamat yang telah di assign dapat mencerminkan nilai current sensor tersebut
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-12-13 11:36 AM
apa ada setting yang lain? aku coba apply signal di embedded analog input logic controller M221 (IN0) yang secara default tegangan range 0 s/d 10 Vdc tapi kok hanya 0 s/d 1.4 Vdc saja yang bisa saya apply . thx untuk bantuannya
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-12-13 04:42 PM
@Anonymous user sudah test pake multimeter tegangannya lebih dari 1.4V ?
Harusnya sih gak perlu ada settingan lagi...
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-12-14 03:34 AM
@Oncom sudah saya cek pake multi bos. tegangannya sesuai yang saya apply kan.
1.4 vdc tampilan di multi juga 1.4.
pas saya apply 1.5 vdc dengan alat calibrator yang saya gunakan langsung protect off. dan sya cek pakai multi calibratornya (tanpa terkoneksi dengan IN0) juga sesuai 1.5 vdc.
apa hardware nya masalah ya?
terima kasih untuk bantuannya
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-12-16 12:51 AM
Coba kita colek expert nya @Anonymous user
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-03-05 07:52 PM
kalo secara multimeternya protect off ada kemungkinan hardwarenya bermasalah, coba diganti yang IN1 apakah sama, saya pernah mencoba untuk volt, tidak ada masalah dan tidak ada tambahan konfigurasi apa2 hanya setting di software configuration nya
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-11-10 10:06 PM
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
apabila sensornya sudah terpasang pada module analognya, bisa juga dengan cara melihat pada nilai integer dari memory address channel analognya ( dengan catatan sensor analognya sudah di scaling dengan benar ) sehingga tampilan nilai integer pada alamat yang telah di assign dapat mencerminkan nilai current sensor tersebut