m221 controling lexium32 servodrive
Hello. I'm new here and to EcoStruxure Machine Expert Basic. I would like to use an M221 (M221C40T) to control a Lexium32 servodrive. In the software, the only way I could find to control it is through the PTO block by sending pulse and direction. Is there any other way, with feedback, to control the servodrive over Modbus, CANopen, Ethernet, by adding an additional module or something? Like how it is possible to control an ATV variable speed drive over Modbus iOSCanner?
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-09-30 12:05 AM
Hello, As you said, there is no other to control lexium 32 with M221 than the PTO objects.
I attached an example application