Hi,
I am using LXM28 with a motor (BCH2). I would like to control the speed of the motor via Modbus, just do simple steps.
I have several issues for the setup:
1/ I can modify P3-06 and P4-07 with the keypad, but they are not permanent.
When I turned off and then turn on the drive, the settings go back to 0 for those parameters.
I used those parameters to be able to force the DI1-5: SON, TQL, SPD0, SPD1, Reset Fault.
Is there a way to make those settings (P3-06 and P4-07) can be saved in eeprom?
2/ With SoMove, I can see the right values of parameters P3.06 and P4.07 only if I turn the flag Exclusive ON.
Can I set the Exclusive flag on via Modbus? (Is the same as Access Lock register?)
3/ Using SOMove, I can't manage to rotate the motor. I thought by turning on SON bit I would start, the motor,
Is there a flag that needs to be turned ON?
SON is on.
SReady is ON
SPD0=1, SPD1=0
P1.09 = 1000
There is no error.
4/ What is the Modbus register to monitor the operating state?
Thank you for you support
Best,
KB
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-20 10:14 PM
For Modbus control of LXM26/28, activate permission first by P10-32(0xB40), then enable via P2-30=1(0x33C), reset fault with P0-01=0(0x102). For jog operations: P10-25(0xB32)=1(JOG+) or P10-25=2(JOG-); P4-05(0x50A)( JOG Velocity)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-20 10:14 PM
For Modbus control of LXM26/28, activate permission first by P10-32(0xB40), then enable via P2-30=1(0x33C), reset fault with P0-01=0(0x102). For jog operations: P10-25(0xB32)=1(JOG+) or P10-25=2(JOG-); P4-05(0x50A)( JOG Velocity)