Posted: 2025-01-29 07:21 AM . Last Modified: 2025-01-31 04:50 AM
Hi, i have a problem with the writing of LXM32iETH drive's registers with function 16 (write multiple holding registers). In particular the problem returns the error 03 (illegal data values). I readed that there is a password that block the external modbus connection. Is there a mode to resolve this problem to disable the password or another methods for to write the registers thorough modbus tcp connection?
Regards.
Salvio Veneziano.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-18 02:30 AM . Last Modified: 2025-02-18 10:55 PM
Hello,
the LXM32iETH is designed to be controlled by PROFINET protocol only. ModbusTCP protocol is only implemented for comissioning software SoMove. ModbusTCP IO Scanning is missing at all. Only single commands may be possible to read and write. There is no Modbus manual for this device. BR Stefan Kuerz
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-19 03:39 AM
Hello, thank you so much for your answer. I have a gateway modbus tcp to profinet, I can use it to comand servo?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.