Posted: ‎2022-10-25 09:59 AM
HI,
I'm trying to write two INT from a BMEH582040 CPU to a BMXP342020 CPU Connected via Ethernet using write_var function block in the H58 program (as in the code attached). The GEST from the write_var shows no error how ever the values of the destination %MW don't change (it's always 0).
I can't find the problem if anybody can help or has an idea i would be very grateful.
thanks in advance.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2022-10-27 04:48 AM . Last Modified: ‎2022-10-27 04:54 AM
Hi!
Looks fine except your ADDM string after IP and the bracket should end with TCP.MBS
Also did you set a timeout inside the GEST on the third word? (in number of 100ms periods, that is a value of 10=1s). Without a timeout the communication can "lockup".
Also does the first GEST word change? If communication is running fine it should show a new value each transmission, in your case every second. Without a timeout set it may not change if it is already in a locked up state.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2022-10-30 12:45 AM
First of all thank you for your reply.
I implemented the changes that you gave me but still the destination array values are 0.
I Still can't find the error.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2022-10-30 01:27 AM . Last Modified: ‎2022-10-30 05:14 AM
Hi Ibrahim,
I see you are using ADDMX function to identify the slave device.
I recommend you use the following: ADDM('0.0.3{192.168.1.11}255') OR ADDM('0.0.3{192.168.1.11}1')
M340 CPU IP Address is 192.168.1.11
Other parameters look fine.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2022-10-31 12:29 AM
Is the first value of GEST updating with new values every sec? Making sure it is running...
I would also try ADDM instead of ADDMX as @ProfHameedi said but ...TCP.MBS should work fine as that is what I always use myself.
I never used ADDMX myself and I really can't see the difference between them.. (maybe ADDMX has more address syntax options?)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2022-11-01 12:17 AM
Btw, where did you read channel should be .3? Documentation about this does not seem very easy to come by but I think it should be .10 for ethernet on the CPU.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2022-11-01 01:25 AM
thought 0.0.3 was related to rack slot channel
M580 channel 1 is service port, channel 2/3 device net, see picture. 0.0.3 seems to be the way to go and it works 🙂
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2022-11-01 01:35 AM . Last Modified: ‎2022-11-01 01:37 AM
Oki, I saw some documentation using .10 but that was not an exact modbus tcp example, it was about setting IP or something I think. I'm not very experienced with M580 either when it comes to FBD communications as I try to use the DTM browser/IO scanning as my first choice for modbus TCP 🙂
Btw, do you know where the documentation for this is or did you find this out by yourself? 🙂
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2022-11-01 04:02 AM
EcoStruxureâ„¢ Control Expert - Communication Block Library https://www.se.com/ww/en/download/document/33002527K01000/
seem to be the go to documentation about this, not that easy to read tho.
On page 74 it says M580: "NOTE: For Modicon M580 CPU, to configure a communication through the CPU
Ethernet port, r=0, m=0 and c=3."
I believe ADDMX is used with M580 PLS if you have a module on an EIO drop, otherwise we should use ADDM. EIO Drop is shown on page 83-84
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2022-11-01 08:16 AM
Nice, didn't find that document before.
On page 62 it say that for *_MX functions the channel is not .3 but .10 for main CPU ethernet so that must be what I was reading about before...
Link copied. Please paste this link to share this article on your social media post.