Ask our Experts
Didn't find what you are looking for? Ask our experts!
New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-28 11:57 AM
I am converting a CTC hmi to a Vijeo project. The previously configured alarms looked at the input address 10001 in Proworks. My understanding is that the 10001 address is an input address assigned to the input card.
I cannot read the 10001 address using the %M10001. When I configure Vijeo to use either the %I or the %IW, I get a config error.
Is it possible to read an input address 10001 or should I remap?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-30 06:57 AM
Jalber,
Here is a cross reference between the Modbus address and the equivalent Control Expert IEC address. Vijeo Designer can use either depending on the driver selection. If you selected IEC syntax, then you will see the references as %I, %IW, %M, %MW (also if you checked the 0 based controller you will be off by one address as a 984 controller is 1 base). If you are using the Modbus/TCP driver you need to set it up as IEC61131 Syntax not checked, Unit ID 255, Low word first, and low byte first under variables. You will then see the 0x, 1x, 3x, 4x references in Vijeo designer instead of the IEC %I when you create a variable.
100001 = %I1
000001 = %M1
300001 = %IW1
400001 = %MW1
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-29 10:17 PM
Try %M0001. I think that will work. What is the PLC?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-30 02:12 AM
Hi Jalber,
"Vijeo" is the brand name of many Schneider products, so I'm not sure which one you are referring to, but many HMI and SCADA products cannot read physical I/O addresses directly. Please copy the data in the PLC to memory adresses to be able to read them.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-30 06:57 AM
Jalber,
Here is a cross reference between the Modbus address and the equivalent Control Expert IEC address. Vijeo Designer can use either depending on the driver selection. If you selected IEC syntax, then you will see the references as %I, %IW, %M, %MW (also if you checked the 0 based controller you will be off by one address as a 984 controller is 1 base). If you are using the Modbus/TCP driver you need to set it up as IEC61131 Syntax not checked, Unit ID 255, Low word first, and low byte first under variables. You will then see the 0x, 1x, 3x, 4x references in Vijeo designer instead of the IEC %I when you create a variable.
100001 = %I1
000001 = %M1
300001 = %IW1
400001 = %MW1
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.