Service Level :199 for BMENUA0100 module

Modicon PAC Forum

A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Modicon PAC Forum
  • Service Level :199 for BMENUA0100 module
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Trinxs1
Lt. Commander Trinxs1 Lt. Commander
10
ciupol
Lieutenant ciupol
9
MatthewM
Lt. Commander MatthewM
8
RoozeeR
Lt. Commander RoozeeR Lt. Commander
8
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Modicon PAC Forum
Sam1987
Crewman Sam1987
Crewman

Posted: ‎2025-07-14 05:10 AM . Last Modified: ‎2025-07-14 02:31 PM

0 Likes
9
192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-14 05:10 AM . Last Modified: ‎2025-07-14 02:31 PM

Service Level :199 for BMENUA0100 module

Hi Experts,

For a BMENUA0100 module installed on rack A the service(Hot standby CPUs) level is 199 and it's not working. The same module in the other racks is working fine and the their service level is 255. Any ideas?

Labels
  • Labels:
  • 02. Modicon M580 ePAC
  • 05. Networking & Communication
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 9
Trinxs1
Lt. Commander Trinxs1 Lt. Commander
Lt. Commander

Posted: ‎2025-07-15 12:41 AM

0 Likes
3
186
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-15 12:41 AM

When the BMENUA0100 module is operational but in the standby PLC rack it will have a service level of 199.  I have not checked this fully, but it will not become fully operational until the CPU and rack becomes the primary CPU.  Try forcing a swap of the primary CPU so that the NUA module becomes the primary and the service level changes to 255.

Please note there is new firmware (V2.04.02) for the BMENUA0100 module that addresses a bug fix with the NUA module in a hot standby system where the service level remains 0.  

Trinxs
Senior Technical Sales Consultant - PAC
Reply

Link copied. Please paste this link to share this article on your social media post.

Sam1987
Crewman Sam1987
Crewman

Posted: ‎2025-07-15 02:15 AM

In response to Trinxs1
0 Likes
2
184
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-15 02:15 AM

Thanks for the reply.

my problem is that for this rack specifically while the cpu is the primary one, the service level is 199!

Reply

Link copied. Please paste this link to share this article on your social media post.

Robert_Willis
Lieutenant JG Robert_Willis Lieutenant JG
Lieutenant JG

Posted: ‎2025-07-15 05:49 AM

In response to Sam1987
0 Likes
1
182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-15 05:49 AM

Please provide the following:

1. ECE Version with hotfixes listed

2. Firmware Version of the M580 CPU

3. Part number of the M580 HSBY CPU

4. Firmware Version of the BMENUA0100

5. How are you reading the Service Level? Are you using the BMENUA0100 Device DDT or directly from the BMENUA0100 via a OPC UA Client?

Reply

Link copied. Please paste this link to share this article on your social media post.

Sam1987
Crewman Sam1987
Crewman

Posted: ‎2025-07-15 07:45 AM

In response to Robert_Willis
0 Likes
0
161
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-15 07:45 AM

thought the other modules in other racks are working (service level:255) with the same Firmware version (2.03.05), I tried to update the Firmware using Automation Device Maintenance to 2.04.02 but I receive an error "firmware update was not successful. the device has declined the firmware update due to an invalid signature or a corrupted or compatible file"

-I am using web browser to read values from the module.

-CPU is eH58-4040

Reply

Link copied. Please paste this link to share this article on your social media post.

Sam1987
Crewman Sam1987
Crewman

Posted: ‎2025-07-17 01:43 PM

0 Likes
0
136
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-17 01:43 PM

I managed to upgrade the firmware. the issue still exist when I install the module on that rack. when I install it on my test rack, service level is 255 and works fine but as soon as I return it back service level goes back to 199 and module cannot communicate!

Reply

Link copied. Please paste this link to share this article on your social media post.

Trinxs1
Lt. Commander Trinxs1 Lt. Commander
Lt. Commander

Posted: ‎2025-07-21 01:40 AM

0 Likes
1
95
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-21 01:40 AM

@Sam1987 as @Robert_Willis has suggested check the firmware version of the CPUs.  It would be best that these are at V4.40.
Is there an issue with the rack that you place the module in? If you swap racks for the NUA does the fault remain with the rack or the module or both?

Trinxs
Senior Technical Sales Consultant - PAC
Reply

Link copied. Please paste this link to share this article on your social media post.

Sam1987
Crewman Sam1987
Crewman

Posted: ‎2025-07-21 03:51 AM

In response to Trinxs1
0 Likes
0
87
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-21 03:51 AM

so it is obviously a bug!! to my surprise, the module installed on the primary rack was communicating with the standby CPU! service level was 199 and when I stopped the standby CPU it changed to 120!! I stopped the CPUs and initiated them but it didn't work. So, during a short shutdown I had to remove power from CPUs and power them on again. now the service level is 255!

Reply

Link copied. Please paste this link to share this article on your social media post.

Sam1987
Crewman Sam1987
Crewman

Posted: ‎2025-07-21 06:20 AM

0 Likes
1
89
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-21 06:20 AM

The service level is 255 but I can't still write to the tags using Uaexpert while I can read them!

Reply

Link copied. Please paste this link to share this article on your social media post.

Robert_Willis
Lieutenant JG Robert_Willis Lieutenant JG
Lieutenant JG

Posted: ‎2025-08-07 05:01 AM

In response to Sam1987
0 Likes
0
8
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-07 05:01 AM

Please check to see that the variable is not being overwritten by application logic.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of